How do you protect your appliances from harm in case of
neutral failure in a three phase power supply set up.
Answers were Sorted based on User's Feedback
Yes if neutral fails in a three phase power supply system
than the single phase voltage may increase. You can fix voltage sensitive suppressors across the supply line in your applances which will short circuit the excess voltage to earth and cause the RCCB to trip and save your appliances from further damage.
| Is This Answer Correct ? | 3 Yes | 0 No |
Whenever neutral fails in three phase system, the connected
loads will get connected between phases owing to floating
neutral.Hence depending on load resistance across these
phases, the voltage keeps varying between 230V to 400V.A
suitable servo stabilizer with wide input voltage range with
high & low cutoff may help in protecting the equipments.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / raj
Simply use ELCB or RCBO as incomer in the 3ph supply system
since if neutral opens it will trip the complete supply
without damaging to the system.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / lokesh ranjith
If nuetral fails in three phase system nuetral floats then
230 volts in will become 420V caused damage to the
equipment
| Is This Answer Correct ? | 2 Yes | 8 No |
can we increase our frequency rate in INDIA?
What are the testing to be done before the installation of 1000 KVA Transformer?
We in my plant one of the transformer showing neutral to earth voltage is 22V how to solve it
why we have to particulary use ACB for below ratings,even available of MCB,MCCB with that range ?
What is rccb?
When will you multiply and devide with derating factors to the actual value while sizing the cable?
What is an ac motor?
what is the effect of back reactive power on the generator ?
how generator generates electricity?
Where is servomechanism used?
which type of A.C motor is used in the fan (ceiling fan, exhaust fan, padestal fan, bracket fan etc) which are find in the houses ?
25 Answers Airtel, MPPTCL, USSA,
can you use 400 volt 3 phase and neutral and earth equipment on 440 3 phase and earth supply safely and if so how?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)