How do you protect your appliances from harm in case of
neutral failure in a three phase power supply set up.
Answers were Sorted based on User's Feedback
Yes if neutral fails in a three phase power supply system
than the single phase voltage may increase. You can fix voltage sensitive suppressors across the supply line in your applances which will short circuit the excess voltage to earth and cause the RCCB to trip and save your appliances from further damage.
| Is This Answer Correct ? | 3 Yes | 0 No |
Whenever neutral fails in three phase system, the connected
loads will get connected between phases owing to floating
neutral.Hence depending on load resistance across these
phases, the voltage keeps varying between 230V to 400V.A
suitable servo stabilizer with wide input voltage range with
high & low cutoff may help in protecting the equipments.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / raj
Simply use ELCB or RCBO as incomer in the 3ph supply system
since if neutral opens it will trip the complete supply
without damaging to the system.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / lokesh ranjith
If nuetral fails in three phase system nuetral floats then
230 volts in will become 420V caused damage to the
equipment
| Is This Answer Correct ? | 2 Yes | 8 No |
The CHARGED BATTERY GET DISCHARGED WHEN IT IS NOT IN USE FOR LONG TIME.GIVE REASON.
During a temperature rise test of a bus duct, it is fed with 415 volts at 2000 amperes. Why dont we get an electric shock if we touch the bus bars?
What are the section criteria for cables. Now everywhere XLPE power cable is used or PVC is also used?.
If a capacitor bank is having rating 750kvar for 6.6kv. Then for 3.3kv how much will be the rating of capacitor bank.
What is spill current in protection relays?
Factory acceptance test. FAT. For 132 kv transmisstion towers what is that meaning and what are the tests commonly companies perform now days.
What is the diffrece between ACB & MCCB
HOW MUCH CURRENT CAN CARRY A 50 kvar DELTA CAPACITOR BANK?
A powerplant has 8 gensets operating in grid parallel mode. In one genset sometimes there is pf variation and kvar variation. The plant operates in pf mode. When this variation is onbserved the load is stable, voltage is also stable, freq and genset speed is also stable. How will you check the functioning of pf card. What shall be the ideal output vdc of the pfc, from there it is input to AVR?
For 415v,3phase,22kw rating of motor how to calculate MCCB rating
how to set time from star to delta starter
what is cause of static electricity? I experience shock when i touch metal equipment in a room ,furher check shows earth leakage showing 80ma at the DB near to the 400 MCCB?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)