How to isolate a DPT from line in the condition that process
must not be disturbed,and process is also critical and no
bypass is available.?
Answers were Sorted based on User's Feedback
Answer / lal
we can set the actual value & activate a Timer from the DCS , within in the time which set on the DCS we can isolate the transmitter from the line , and it will not affect the process , the timer is used for safety purpose , we cannot activate it more than a limited time.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / muhammad arsalan afzal
isolate the transmitter from the main isolation valve and
follow this procedure.
First of all
1= Close high pressure manifold valve
2= open the equilizing valve
3= than close the low pressure manifold valve.
Mostly we we open equilizer valve when we are isolating
the tx. but what will happen if we close high side pressure
valve before equilizing valve? applied process Pressure is
already there on both sides of the transmitters no extra
pressure will be exerted on the tx because we are only
closing the valve. DP cell demage only in that case if we
purge high or low side before closing the manifold
isolation valves and we start closing the valve without
opening the equilizer.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / vinu joseph
first close the process isolation valve.then slowly equlise the pressure using equalising valve in the manifold.thendrain the transmitter and we can remove it from service
| Is This Answer Correct ? | 4 Yes | 5 No |
Answer / m.abouraya
1-open the equalizer and then open the isolation valves
(high wth low) and then make the drain
| Is This Answer Correct ? | 1 Yes | 5 No |
What are different type of instrument cable
diff c and c++
why does a transmitter o/o signal starts from 3-15psi or 4- 20mA?
how eddy current loss in probe and induced gap voltage accros probe trip and shaft
You wish to SINK all my digital inputs to a PLC digital input card. Would you common out the leads to a positive or a negative connection?
meaning of SMART
What is an analog input - output , digital input - output . Any example ???? How they r known its ai-ao or di - do
1 > HOW TO MEASURE INTERFACE LEVEL 2 > DIFFERENCE BETWEEN RADAR & ULTRASONIC LEVEL TRANSMITTER
How many mode are in ups?
whey we conect ammeter in series and voltmeter in parallel in circuit
i have one absolute pressure transmitter for the range is -400mmhg to 400mmhg. If i do the zero trim at atmosphere the transmitter should be give 4ma or 12ma? which one is correct?
Which tank weighing system is better to install (Accuracy point of view) 1) Tank weighing system with 3 load cell or 2) Tank weighing system with 4 Load cell
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)