why the under of transformer platform is filled with rock stones.
Answers were Sorted based on User's Feedback
Answer / rk
TO REDUCE THE FIRE HAZARD DURING OIL LEAKAGE OR OIL
SPILLOVER DURING ANY UTWANTED SITUATIONS FOR INSTANCES SHORT
CKT. INSIDE TRANSFORMER. OIL IS FLAMMABLE IN NATURE.
| Is This Answer Correct ? | 21 Yes | 6 No |
Answer / rajeshsan
There are many reasons for using gravel stones of 60mm size below transformer. Few are:-
1. During oil spillage from transformer or during sprinkler system act the water draining from soak pit it will be easier.
2. To avoid the grown of grass and entry of animals etc.,
3. To reduce the step potential
You can please refer the NFPA 850 for details.
| Is This Answer Correct ? | 14 Yes | 3 No |
Answer / santhosh (saint-gobain)
1. Avoid water stagnent under transformer,
2. Vibration absorption,
3. Stones having no conductivity..
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / m.kumaran
because reduce the step potential while short circuit timing
| Is This Answer Correct ? | 8 Yes | 10 No |
Answer / suresh babu
first to prevent the stagnent of water under the transformer
second vibration withstand
third low resistivity i mean rock stones forms low
resitivity path
| Is This Answer Correct ? | 2 Yes | 7 No |
Answer / baljeet singh
To reduce the short circuit current when fault occurs in transformer
| Is This Answer Correct ? | 3 Yes | 10 No |
Answer / raghu
The stones will absorb the vibrations from the transformers
and other switch gear equipemts..
| Is This Answer Correct ? | 5 Yes | 14 No |
Answer / talluri
Rock will protect substation from electrical damages
| Is This Answer Correct ? | 0 Yes | 12 No |
Answer / shahul
To avoid the snake and other insect enter inside the
transformer structure and also avoid water flooding
under the transformer during the rainy season
| Is This Answer Correct ? | 4 Yes | 20 No |
ASTM D 3455 - Standard Test Methods for Compatibility of Construction Material with Electrical Insulating Oil of Petroleum Origin has been used for Testing Transformer Oils with a product placed in it. Aged Control Oil has a Power Factor of 0.032% at 100°C. Aged Oil with a Test component has a Power Factor of 0.093% at 100°. Is this increase acceptable? If not why? How much increase is acceptable?
How we calculate airgap between phases & terminal box of the transformer? any formulae.
what is maintenance?how to explain
I have 480V Single phase and I am trying to figure how big of a transformer (KVA's) and Primary breaker size I need to provide 200 Amps at 240V for a building.
Name a govt approved university which have 100% online engineering course.
for compensate 315mh inductance ,how many capaciance required?
I decided to provide a 11KV / 440V Xformer in my Substaion. What are the protection required for that?
what is the mager value of star motor and delta motor between phase to ground and phase to phase, and minimum how much should be value ?
How to calculate the breaking capacity(like 15ka,20ka) of Circuit breaker (MCB,MCCB,ACB)
9 Answers Career Excellent Sdn Bhd, Neona, Northern Max Engineering, Sps Renewables, Terasaki, UEM,
why for transformer protection we protect tranformer from 3rd hormonics and 5th hormonics and what is the reason of generating these horminics in electrical system?
what is the difference between watts and volts?
If the battery is in charging condition means, battery is which type of load? Capacitive or Resistive load?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)