I decided to provide a 11KV / 440V Xformer in my Substaion.
What are the protection required for that?
Answers were Sorted based on User's Feedback
Answer / ajay
for H.V side u can use R.M.U whc include SF6 C.B and For LT
side ACB
Is This Answer Correct ? | 4 Yes | 3 No |
Answer / nirajan poudel
11000/440v means it is step-down transformer.so, for MV
side use 9kv LA,11 kvDO-FUSE and switch gear panel which
includes VCB which is used for isolating the transformer
during maintenance period.For LV side use TP MCCB for 3-
phase bus bar(R,Y,B) and use SP MCCB for 1-phase bus
bar.And there must be provision for AMF (Automatic Main
Failure Panel) to change the supply from main line to stand-
by generator and vice-versa with respective CB tripped.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ajay pal
transformer are to be fully earthed ,neutral grounding
resistor are to be provided, transformer overhead
differential protection , transformer oil for cooling is
very necessary ,
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / doli tomar
11000/440v means it is step-down transformer.so, for MV
side use 9kv LA,11 kvDO-FUSE and switch gear panel which
includes VCB which is used for isolating the transformer
during maintenance period.For LV side use 4P ACB /MCCB for
3-
phase bus bar(R,Y,B) and use overcurrent, overvoltage,
undervoltage,IDMT,Single phase preventer,restricted earth
fault relay because Relays are used where it is necessary
to control a circuit by a low-power signal (with complete
electrical isolation between control and controlled
circuits), or where several circuits must be controlled by
one signal.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / rakesh
Transformer Secondary star neutral need to be earthed.
Separate earthing pit need to be provided.
Is This Answer Correct ? | 3 Yes | 6 No |
how many types of ratings are there of transformer
I have 30 kw motor load & i have selected 10 kvar capacitor bank for power factor improvement.my existing p.f is 0.85 & proposed p.f is 0.99 so ,is it right selection? 2 nd question how to connect c.bank whether in delta or star connection & how to decide it?
WHERE CAN I GET THE PREVIOUS QUESTION PAPERS OF Govt Polytechnic in deee 2nd year papers
how it can be decided what will be the rating of CT and PT to be used in LT or HT cables?
What fomula is used to calculate: 1. rated frequency withstand voltage, and 2. rated lightning impulse withstand voltage.
HI SIR, AM PREPARING FOR RRB FOR SECTION ENGINEER POST. PLZ SEND ME THE PREVIOUS QUESTION PAPERS AND HELP ME. I HAVE NO ENOUGH TIME MY EXAM DATE IS 22ND JUNE.... MY EMAIL ID IS nalla.amarnath@gmail.com
What is the percentage loss for aluminium wire for HT line more than 11KVa
Send me Model Question paper for the post Scientific Assistant in NPCIL
hi sir i have load of 17.5kw in 3 phase lighting circuit which mcb i can use
in ACB breaker requireding 3200Amps. buscoupler getting OFF mode and again it reset and getting normal position give me a required answer?
to improve the existing power factor whether capacitors have to be added in series or parallel.and why
state types of reflectors in illumination engg. ???????