Answer / shan80

it depend upon the value of current flows during short
circuit.
And the short circuit current depends upon the KVA rating of
transformer how supplies that particular load and transformer
percentage impedance.

Is This Answer Correct ?    56 Yes 15 No

How to calculate the breaking capacity(like 15ka,20ka) of Circuit breaker (MCB,MCCB,ACB)..

Answer / jitesh patel

we must know load of perticular equipment.
For Ex. Our load in MVA is 50 MVA
Our system voltage(MCB,MCCB,ACB) is 440V.

I(Bre)= 50/(1.73x0.440)=65.6 =Approx 65KA.

Our load in MVA is 20 MVA
Our system voltage(MCB,MCCB,ACB) is 440V.

I(Bre)= 20/(1.73x0.440)=26.2 =Approx 25KA.

Is This Answer Correct ?    79 Yes 50 No

How to calculate the breaking capacity(like 15ka,20ka) of Circuit breaker (MCB,MCCB,ACB)..

Answer / ali

100A MCCB Bteaking capacity calculation

Is This Answer Correct ?    16 Yes 4 No

How to calculate the breaking capacity(like 15ka,20ka) of Circuit breaker (MCB,MCCB,ACB)..

Answer / mohammed rafi

All above said suggestions are mere copy paste of something from wiki answer.its totally wrong.
Aforesaid calculations are to calculate rated current.
Short circuit analysis is to be done to calculate breaking capacity.

Is This Answer Correct ?    11 Yes 3 No

How to calculate the breaking capacity(like 15ka,20ka) of Circuit breaker (MCB,MCCB,ACB)..

Answer / ashok

it depends on the short circuit & full load of equipment

Is This Answer Correct ?    24 Yes 20 No

How to calculate the breaking capacity(like 15ka,20ka) of Circuit breaker (MCB,MCCB,ACB)..

Answer / ranadhir roy

We need to find out the short circuit MVA & based on this shortcircuit MVA , we need to calculate shortcircuit current .

Is This Answer Correct ?    2 Yes 0 No

How to calculate the breaking capacity(like 15ka,20ka) of Circuit breaker (MCB,MCCB,ACB)..

Answer / sunil sethi

All are ok, but In industries generally 5MVA transformer they are using for a company load, then if we consider 5MVA is our load then Icu is 5/(1.732x440)=0.0065ka , please clarify, Is it ok please answer .

Is This Answer Correct ?    2 Yes 3 No

How to calculate the breaking capacity(like 15ka,20ka) of Circuit breaker (MCB,MCCB,ACB)..

Answer / t s gupta

Breaking Capacity of MCCB is pre-calculated permissible amount of fault current (value of current can flow from contacts before opening/tripping the MCCB without damaging) which may facilitate the safe operation of MCCB and distribution transformer both.
It shall be calculated/derived from the distribution Transformer MVA rating and %impedance = kVA*100/ system voltage of load side * % Impedance rating
e.g. 20 kVA transformer with 5% Impedance, secondary voltage 440V i.e. 0.440 kV
Fault current Isc = 20*100/.440*5 = 10kA approx.

Is This Answer Correct ?    0 Yes 1 No

How to calculate the breaking capacity(like 15ka,20ka) of Circuit breaker (MCB,MCCB,ACB)..

Answer / hrusikesh dehury

we must know load of perticular equipment.
For Ex. Our load in MVA is 50 MVA
Our system voltage(MCB,MCCB,ACB) is 440V.

I(Bre)= 50/(1.73x0.440)=65.6 =Approx 65KA.

Our load in MVA is 20 MVA
Our system voltage(MCB,MCCB,ACB) is 440V.

I(Bre)= 20/(1.73x0.440)=26.2 =Approx 25KA.

Is This Answer Correct ?    14 Yes 24 No

Post New Answer

More Electrical Engineering Interview Questions

What makes the difference between 50Hz supply and 60Hz supply which one is economical and how can you support your answer...........?

2 Answers   Fertichem, Kuwait Oil Company,


What is the function of a capaitor in 1-phase IM?

1 Answers  


DEAR SIR/MADAM,CLEARLY EXPLAIN ABOUT CRAWLING AND COGGING EFFECTS IN INDUCTION MOTOR.

0 Answers  


What is signal flow graph?

0 Answers  


What is servo motor? what is its purpose?

0 Answers  






Can any body tell me the different types of LT cables & their application.

0 Answers  


how many units will 100 kvar capacitor consume for one day?

2 Answers   Philips,


we erected (48HP)63kva dist transformer and incoming from 11kv line,out going is 415v domastic line 2.04 km.for that actual output current is 84A. what are the losses and final output current.

3 Answers   Essar,


what will be the effect of leading power factor on turbogenerator (and system) that is running parallel with other TG.

1 Answers  


Explain about Leakage Test.

0 Answers  


What is meant by Im=30mA@Vk/2. How to know the kee point voltage for CT design

0 Answers  


how hydrogen cooled alternator undergo maintanence ? that is hydrogen when come in contact with air can result into explosions .

0 Answers   DVC,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)