How we calculate airgap between phases & terminal box of
the transformer? any formulae.
Answer / dr rajan
There is no formula. It is always a thumb rule. The dielectric
break down of air is about 6kv/cm of gap. So depending on the
terminal voltage, use a rational distance keeping in mind the
connecting terminal dimensions of the cable. An average of 15
cm space between phases in 11Kv accepted as a practice.
| Is This Answer Correct ? | 2 Yes | 1 No |
what is the standard values(Megger test) of resistances between L&N,L&E and N&E for a system on IEE regulations?
previous year paper of ntpc bhel for degree in electrical enng
what are the protections used in power transformers of 5 mva and above
explain the meaning of harmonic resonance
Is there possible to Test Transformer for Overfluxing Capability. Or is there any firm who does Overfluxing Test on Transformer?
1. Why a DC motor starter is called 3 point starter
21 Answers ABB, CG, College School Exams Tests, Crompton Greaves, Infosys, Siva,
what are balanced and unbalanced loads
what is mean by ideal infinite bus? why it is required to consider in fault short circuit calculations?
IF avr is voltage regulator of genset means why we are giving genset CT sense to AVR ?
what is leading power?
what is the distance between two overhead lines
what will be the minimum megger value for 132 Kv (earthed) potential transformer
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)