What are the possible causes of REF operation on a power
transformer
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
All cts(Phases and neutral) are connected in parallel.If
there are unbalanced currents in phases, the resultant
current in REFR is zero as the difference is also measured
by NCT .If there is an earth fault inside the transformer
or between cts and bushings ,the fault current is sensed by
NCT only. Hence current balnce is lost in REFR resulting in
trip command by the relay
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / k.prakashchandra
Please note that REFR will not act under earth faults in
phases beyond the CTs. As its coverage is limited
(restricted) to Tr only ,it is called ristricted earth
fault relay.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / k.prakashchandra
An earth fault between CTs of primary and secondary sides,
as the fault current will not pass through secondary side CT
Is This Answer Correct ? | 2 Yes | 2 No |
actually i dont know the answer but i wanted to know what
is the REF operation of power x'mer...plz explain in detail
Is This Answer Correct ? | 1 Yes | 1 No |
we have provided 30 nos. relay contacts in panel.I want to know how do we do the numbering for the relay contacts as per any applicable standards
please tell me how a surge protector work on a DC 48Volt.? please describe briefly.
whu the transformer noise during running condition?
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?
Can you use step up generator transformer of voltage ratio 16.5kv/420kv in place of step up generator transformer 15.75kv / 420 kv
is it possible to flow a current between nutral and earth in a circuit? although nutral and earth having same potential diffrence? i=0/r=0A if any body now any solid reason because i am getting a triping problem in rcbo due to nutral and earth shorting???
what is meant by cbct elr?
What is the possible cause for failure of lightning arrestors in outdoor substation under normal condition
what is the importance of creepage distance in disc insulators
What voltage is used in Directional earth fault relay? and why?
Difference between on line capacitor and Station type capacitor
why in India it is maintained for exactly 50HZ frequency, why it is not that 49Hz,why it is so?