Answer / k.prakashchandra
All cts(Phases and neutral) are connected in parallel.If
there are unbalanced currents in phases, the resultant
current in REFR is zero as the difference is also measured
by NCT .If there is an earth fault inside the transformer
or between cts and bushings ,the fault current is sensed by
NCT only. Hence current balnce is lost in REFR resulting in
trip command by the relay
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / k.prakashchandra
Please note that REFR will not act under earth faults in
phases beyond the CTs. As its coverage is limited
(restricted) to Tr only ,it is called ristricted earth
fault relay.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / k.prakashchandra
An earth fault between CTs of primary and secondary sides,
as the fault current will not pass through secondary side CT
| Is This Answer Correct ? | 2 Yes | 2 No |
actually i dont know the answer but i wanted to know what
is the REF operation of power x'mer...plz explain in detail
| Is This Answer Correct ? | 1 Yes | 1 No |
What is effect of over voltage and under voltage on ACB
Why we are not placing c.B 's btwn generator and transformer.? what happens when generator gets disconnected from transformer when it is running @ full load?
How the CT and PT ratings are calculated
What is corona loss?
What is meant by term Back to back in HVDC transmission?
i have ht transformer of 142 kva with air cooled facility,having secondary voltage 7850volt, and secondary connected full way bridge rectifier .i faced the problem repeatedly that transformer one coil and rectifier diode of two phase was burnt two times. i checked all the secondary ckt. no any short ckt found,then what will be the cause side
2 Answers Modern Terry Towels,
what is Micrologic 6.0A advantages over Micrologic 2.0A
what is the different between earth leakage relay and earth fault relay?
how define the torque in ac drive. from electrical side in the drive friquency ,voltage and current three factor is there.
how to can we synchronize different capacity of DG sets.60kva& 250kva?
can you send me the placement papers of electrical engg. from companis like NTPC,DRDO,IOCL,HPCL,BPCL etc.?If,plz send as soon as possible.Thanks.
why a tester wont shock while testing the power in house
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)