how the 4 to 20 mA signal goes to any
controller/indicator,and what is the role of voltage ,12/24
and how to do connection of it, in controller.
Answer / carl_ellis
For a 2 wire loop powered transmitter, a DC power supply
supplies power to the transmitter to power its electronics.
The transmitter uses about 3.5mA of the loop current to run
its electronics.
The transmitter's electronics measures a physical property
(temperature/pressure) which creates a measurement value
associated with engineering units. The transmitter
regulates the loop current between 4.0 and 20.0 mA (by
varying its internal resistance to drop whatever voltage is
needed to create the correct current) so the current
represents a measurement proportional to the scale
configured for that physical property.
The controller/indicator is the primary 'load' with an
analog input that has a dropping resistor. The dropping
resistor creates an IR (voltage) drop the
controller/indicator uses for its A/D conversion.
A 2 wire loop powered transmitter has a lift-off voltage,
the minimum voltage needed to operate the transmitter with a
zero ohm load. As the loop load voltage increases, the
minimum voltage required to power the transmitter and the
loop load increases.
24Vdc is the typical, nominal power supply voltage used in
the process industries. Many 2 wire loop powered
transmitters will function with supply voltages up to about
40Vdc. Higher supply voltages are needed with long copper
wire runs where the wire resistance becomes a significant
load factor.
Carl Ellis
Measure First
Is This Answer Correct ? | 0 Yes | 0 No |
Reason for capillary type dp level transmitter fluctuation
uses of profibus?
what is the principle of vibration
IN CONTROL VALVE SPECIFICATIONS GENERALLY TERM " DE- 200" ."DM -400"USED,, WHAT IS DE/ DM STANDS FOR?
WHAT IS THIS INSTRUMENTATION?
If a control valve is hunting means means if we are giving 50% to the cv, the cv will open at 51% then slowly slwoly it will reaches 49% , then it will reaches again 50%, this type of action occured frequntly.. so what to do for solve this problem. The possible cause is in volume booster or positioner's relay.. positioner is double acting .. and make siemens..sipart.The cv is double acting and mounted for anti surge operation, it having 4 nos. volume booster, one sov, one positioner, etc..?
2 Answers Gujarat Fluorochemicals Limited (GFL), Shell,
why we are using boosters at glass furnace is there any other thing?
what is power factor?
what is difference between venturi and orifice
how ranges is decided for drum level or dearator level,in my pplant i have seen for boiler drum range is -1000 to 1000mmwc, while for dearator -2000 to 0 mmwc ,why they decided to take this range ?
Before erect the instrument what should you do?
What is an analog input-output
10 Answers TN, Torrent Pharma,