we are used SAMSON 3730 Smart positioner.please tell me how to calibration this.
Answer / chanchal
at first check the air supply.if it is ok then
feed the 4mA by using calibrator in i/p converter of positioner. if valve is zero position(fully closed) then its ok.if valve is not in zero position(fully closed) then set the zero position in positioner by using zero point screw.
next feed the 20mA by using calibrator in i/p converter of positioner.if valve is 100% open then its ok.if valve is not 100% open. then adjust the span setting by using span screwin positioner.
then check 25%,50%,and 75% open position in valve by feeding 8mA,12mA,and 16mA by using calibrator in same way.
Is This Answer Correct ? | 4 Yes | 5 No |
What is the exact output of eddy current proximity probe? For vibration mesurment?
HOW CREATED LP & HP PRESURES IN DRUM FOR DRUM LEVEL MEASUREMENT!
what is meant by turn down ratio?
Dear friends, I have a question: We work on a project which has some boilers to provide steam for desalination unit. The boiler area is safe and the only hazard source is the fuel lines of boilers. I want to know according to NFPA standard which type of instrument should be selected on the fuel line: Eex Type or Non-Eex type? Thanks in advance
Explain pH, Conductivity.
steps for installing orifice plate?
0 Answers Bhushan Power Steel,
How ejector(or)evactor air pump is working in thermal power plant?
what happens when the profibus fails while in operation (operation of a valve)?
1)What is the suitable MOC for flow meters working at temperature between 200 - 250 cen. 2)In which application the mass flow meters are not advisable 3)Is it advisable to use radiation type or radar type instrument for non contact application
Why drum level range is given -500 to 0 mmwc pls give me that answer
what is a good line as ic engineer as maintenance ,oc, project, calibration ,validation engineer?
How to calculate the flow rate in Vortex flow meter?What is K factor?Can you give me an example calculation to understand the same as better?