How to calculate the breaking capacity(like 15ka,20ka) of
Circuit breaker (MCB,MCCB,ACB)
Answer Posted / t s gupta
Breaking Capacity of MCCB is pre-calculated permissible amount of fault current (value of current can flow from contacts before opening/tripping the MCCB without damaging) which may facilitate the safe operation of MCCB and distribution transformer both.
It shall be calculated/derived from the distribution Transformer MVA rating and %impedance = kVA*100/ system voltage of load side * % Impedance rating
e.g. 20 kVA transformer with 5% Impedance, secondary voltage 440V i.e. 0.440 kV
Fault current Isc = 20*100/.440*5 = 10kA approx.
Is This Answer Correct ? | 0 Yes | 1 No |
Post New Answer View All Answers
what are types of encoder
how to calculate vfd o/p voltage by frequency
Define end float in a motor?
Is there any rule to select the voltage of motor based on KW rating? What is the rating above which lt motor becomes the HT motor?.
What is ideal IR values for ground and neutral.
IN dc capacitive reactance is??
How we can come to know the substation range,without go through any name plate ?
What are PLC leader logic program method
1- XC and the RC time constant are both measures of the reaction of C to a change in ____? 2-The power factor is a numerical ratio with a value between 0 and 1 equal to the ______________ of the phase angle. 3-When V and I are out of phase because of reactance, the product of V times I is called ______________ power 4-For _____________ inductors, the branch currents can be added algebraically. 5- The ______________ power in watts can be calculated as I^2R 6-Calculate XL with L = 30mH and f = 1kHz ( I have Xl=2piFL 2*3.141592653*1kHz*30mH =188 ohms Please check) 7-A parallel RL circuit has the values, R = 5kohms, XL = 5kohms. A voltage source of Vt = 10Vrms is connected in parallel to R and L. Determine the total current, It delivered by the voltage source Vt. 8-A series RC circuit has R = 1Mohm and C = 1microF. How long would it take for the capacitor to fully discharge if it is initially fully charged? 9-A circuit has real power = 300W and an apparent power of 500VA. Determine the power factor and phase angle. 10-The time constant for an LR series circuit is T = 0.1s and R = 10ohms. Calculate the inductance L.
What is the difference between diode and a transistor in terms of the direction of current flow?
what is a reactive power? what is the relation with power factor?
Explain what is rated speed?
Define piezo-electric effect?
How to calculate energy stored in a capacitance
Dear All we are having a problem in G120 BOP showing alarm A0503, F0052, F0060 we can not remove fault alarm ,Please any body help us. kowsar