How to calculate the breaking capacity(like 15ka,20ka) of
Circuit breaker (MCB,MCCB,ACB)
Answer Posted / mohammed rafi
All above said suggestions are mere copy paste of something from wiki answer.its totally wrong.
Aforesaid calculations are to calculate rated current.
Short circuit analysis is to be done to calculate breaking capacity.
| Is This Answer Correct ? | 11 Yes | 3 No |