Answer / subharaj
PS Class CTs are used for Differential protection & 5P10
are used for other protection.
| Is This Answer Correct ? | 18 Yes | 0 No |
Answer / k. sankaraiah
calss 5p10 used for normal protection, but PS class used
for special protection. 5p10 is used for non balance
circuits but PS class used for balance circuit.where ever
circulating current is balanced at that time only Ps class
using.This can be used only two CTs are present. Ex.
Differential protection & REF.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / k.prakashchandra
5P10 ct belongs to PS ct group,being specified
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / jonnalagadda chowdary
PS Class CTs are used for Differential,over current
protection(direct protection) & 5P10 are used for restricted
earth fault(indirect protection)
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / fikizolo
Theres basicly no difference, they both overcurrent protection CT's
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / chirag
class ps ct's are special class ct's which are used in
protection where high accuracy is required other than that
5p10 are used.accuracy of 5p10 is less than class ps ct's.
| Is This Answer Correct ? | 2 Yes | 7 No |
Answer / satya dev
Class PS CTs are used for Metering system & Class 5P10 used
for Protection
| Is This Answer Correct ? | 1 Yes | 19 No |
IN a transformer during power supply how the LV and HV bushing works??
Why a transformer Noise during its running condition ?
can anyone please help me to find the rupturing or breaking capacity in KA of circuit breaker (MCCB,VCB,ACB etc) of HT and LT side of a distribution transformer...please help with detailed step by step answer...thank you
for opening electrical shop, tips needed.
what is tha gap between the pole of 132kv line
HOw can we calculate power factor at HT side.
If 440 V supply has given at the secondary winding of transformer at that time if we apply 11 KV at primery then what will happen???????
what is the meaning of impedance protected in instrument cooling fan
What are the maximum and minimum ratings of MCB,MCCB,ACB,OCB,VCB and SF6 breakers?
2 Answers ABB, SK E&C, Sodexo,
a 230v transformer with step down ratio 19:1.it has 2000turns on primary and rated 25va calculate max primary current no of secondary turns volts/turn
which circuit breaker enclosure is best for maintenance guy? 16 bolt & 20 bolt squre or 16,20 bolt hinge
what is motor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)