During the main stator winding insulation testing (phase to ground)of 11kv alternator (Lerysomer) i found 0 and resistance with multimeter and found 20 killo ohm while the power cables are connected both end (Generator & VCB). In VCB PT (Potential transformer) are connected.
Please any body explain that method of insulation is correct or not? also describe of PT connections
Supposing that you have disconnected the neutral of GEN , you will measure the dc resistance of PT as the other end of it is earthed . 20 K ohm will be measured as 0 M ohm by the megger . If you want to test insulation of GEN , you have to isolate the winding from everything .
| Is This Answer Correct ? | 0 Yes | 0 No |
Why transformer is rated in kva?
How to check it good or bad capacitor
WHAT AC (HI VOLTAGE TEST) VOLTAGE SHOULD APPLY FOR 33KV CABLES.EXPLAIN IN DETAIL
In a circuit a capacitor (paper capacitor ) was burned due to over voltage in this case can we replace that type cappacitor with other tye capacitor ?
what is the use of expulsition protective gap in 11Kv line.
What is VCB? where it is installed at SP. What is SP?
Why negative feedback is preferred in the control system?
why told ' x ' mer to transformer
If OLTC is in manual position there is chance to variation of voltage(Low or High)?
Which one is correct mVA or MVA. Whether both the units are same for the transformer
what is KWH
In single phase capacitor motor, if the motor rotate reverse direction then how much power will be consumed by the motor and why?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)