What is the diffrence in between Class PS & Class 5P10 for
CTs
Answer Posted / k. sankaraiah
calss 5p10 used for normal protection, but PS class used
for special protection. 5p10 is used for non balance
circuits but PS class used for balance circuit.where ever
circulating current is balanced at that time only Ps class
using.This can be used only two CTs are present. Ex.
Differential protection & REF.
| Is This Answer Correct ? | 1 Yes | 1 No |
Post New Answer View All Answers
can indirect loading be called as phantom loading?
How can claculate to attain the desired PF in the line ( HOW Much KVAR is required ) Pls Give the formula? Equate Petrochemical 0 1 how to calculate sizing of NGTR (Transformer rating,Loading resistor value and Current rating of resistor) and what is the X/R ratio. Details : 11kV,Capacitance 1.73532 micro farads,40kA for 1sec. 0 1 What will happened. if we feed 3phase supplay to the stater with out insert the rotor. How much current will flow through the stater winnding? Equate Petrochemical 0 1 What is required of exietation to the alternater. 0 1 why star point of HT motor not earthed? Equate Petrochemical 0 1 Why we are getting low voltage in star connection? Equate Petrochemical 0 2 What's ND relay & it's functions? Equate Petrochemical 0 2 How instantanious short circuit current is calculated? its formula? Equate Petrochemical 0 2 What is servo Motor? What's the advantages of this motor over Induction motor? Equate Petrochemical 0 2 What is core CT & it's function? Equate Petrochemical 0 3 what is meant by star/delta voltages as 440/220 in a 3 phase induction motor, and why it should be connected on STAR IN 3 PHASE SUPPLY L & T 0 4 What is required of exietation to the alternater. KNB 1 23 what is the design voltage for 6.6KV 2000 KVAR HT capacitor? Consultancy 0 3 Pls explain about vfd control?Where it is used, Give some example? siemens 1 22 Please explain me abt PQ diagaram in the power sector. 0 9
What is the ratio of true power to apparent power in an ac circuit?
how we can adjust for three phase motor cold stall time ,hot stall time and thermal register set up?
What is the height of DA, DAL, DB, DC & DDE tower?
how could we calculate the no of outgoings from a 800 watt distribution board
How maesure earth neutral value & how much maximum value value required in between earth & neutral.
what is the earth current,reverse power,electrical trip generator short circuit,low voltage, high voltage please discribe me
in india per day how much power is generated including all power station
what is the criterion for selecting vector group of Transformers ? i mean how to decide vector group of Generator transformer, substation trasformer and transformer at consumer end
how to interlock 3 incomer-ACB,1 buscoupler ACB,... pls answer this question and if possible send me the ckt diagram..haifriends2910@gmail.com
what is current check gurd relay?
hi frnds...pls send me aptransco previous papers .....pls..pls,,,(madhar.rocking@gmail.com)and suggest me some websites
What will happen if i used 11KV earth ht kit to 11 KV / 11 KV cable termination?
How do you select the pickup value of the relay?