HOW TO FIND THE PRIMARY AND SECONDARY OF TRANSFORMER(IN OFF
CONDITION) USING MULTIMETER? IS IT POSSIBLE FIND BY SEEING
RESISTANCE???
Answers were Sorted based on User's Feedback
Answer / r.nandha kumar
yes,it is possible by measuring the winding resistance of
primary & secondary.High voltage side will have high
resistance value than th low voltage side
| Is This Answer Correct ? | 36 Yes | 4 No |
as per working principle transformer , there is no primary &
secondary of transformer . transformer can be work in either
ways.
but if we have to check HV & LV we can do with multimeter .
as per transformer ratio
V1/V2=N1/N2=I2/I1. ................eqn 1
&
R =rho L/A . ...............eqn 2
\
as LV side requirement of current more & no of turns are
less , & cross sectional area of conductor is lare as per
eqn no.1& 2,resistance offered by conductor is less as
compare to HV .
| Is This Answer Correct ? | 11 Yes | 0 No |
Answer / desingurajan
initially transformer have no primary or secondary. wherever we giving input, that is called primary. and another end is called as secondary......
| Is This Answer Correct ? | 23 Yes | 20 No |
Answer / rsbangra
As looking the tranformer one side primary and other side
secondary as per name plate, we can mesure resistenance by
just r=v/i v=rating voltage and i= rating current ,voltage
take root 3 of line voltage, so we recive resistanse value
ht or lt side, as other view insulatior are used ht side so
high and lt side lower leanth and small size.
| Is This Answer Correct ? | 3 Yes | 3 No |
Why CT secondary is grounded?
where to use CT and PT?
As per IS why should the control be taken only from R phase, why not from B or Y phase??!!
Direction of flow of active power and reactive power with logic?
How much amps carry in single phase R-phase,in D63A 4-pole MCB
what is an oscillator?
in 5 mva transformer 33/11 kv s/s what rating of capacitor bank is required & what is the fourmula for rating
why we use RYB phase sequence? and somewhere we use UVW ? why?
6 Answers CSPDCL-Chhattisgarh State Power Distribution Company Limited, MUET, TCS,
how a synchronous motor is used as a resistor,capacitor and an inductor?
What is the power factor of a transformer at no load?
What are the causes of unbalanced current on 34.5kv feeder Ia=0.05,Ib= 0.25, Ic=0.15 and In=0.27 prior to tripping current are balance?
In a Capacitor the electric charge is stored in:
2 Answers TELK Transformers And Electricals Kerala Limited,
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)