what is the size of ht cable of 33kv ht line and
transformers ratings are 2.5mva and 5.5mva.please send
formula also.
Answer / eng. d
first, how will you install it?
underground direct buried, inside trenchs or above ground
any ways, the way to calculate will be done by the cable
vendor but you can do rough estimation
for 2.5 MVA transformer
= 2.5MVA/(1.73*33KV)=43 A
then cable shall be derated and much more than transformer
then we can say we select 60A cable rating
then we go to cable vendor catalog
try to see this
http://www.doncastercables.com/cableCalculator.asp
thank you
Is This Answer Correct ? | 10 Yes | 1 No |
what is meant by differential protection of transformer
please send me last 5 year interview questions
How does an oscillator differ from an amplifier?
how much power consumed by 1.5 ton capacity split A.C in 1 hour
in ceiling fan and table fan what is the rotating part and what is the stationary part?
What are the types of Bus bar?
STATE WORKING OF VACCUM CIRCUIT BRAKER?
how will you calculate rated Primary and Secondary voltage and Current for 2500 KVA, 11kv/443V Transformer
To prevent the mal operation of a differentially connected relay while energizing a transformer, the relay restraining coil is baised with (a)second harmonic current (b)fifth harmonic current (c)third harmonic current (d)seventh harmonic current
what is automatic voltage regulator and it is used?
PLease anyone can tell me CTUM-15 specification?
For the same power rating,which motor is bigger in size,AC or DC?