how to syncronize two dg sets
Answers were Sorted based on User's Feedback
Answer / shri..
1) first start the both DG set.
2) Then check Phase sequence R,Y,B
3) check the LL voltage & LN voltage. (both DG voltage
should same)
4) Check The engine RPM (both engine RPM should same)
5) Check The Frequency (both DG Frequency should same)
6) Then close the both breaker.
7) then cross check the voltage,Frequency,RPM
| Is This Answer Correct ? | 9 Yes | 1 No |
Answer / santhosh
DG Sets with equal Voltage, Frequence and RPM should be
connected to a single bus with equal polarity and phase
sequence. Both the DG's should be protected with protecting
devices like breakers.
DG's should be operated in such a way that is starting only
one DG should get ON and as the load crosses 75% of the
capacity of DG then the second DG should get ON.
This will help in minimisng the consumption of fuel, Load
sharing and improves the performance of DG.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / satender
you have first of all Start stop the DG's in manual mode ,
then check the voltage biasing and speed biasing by running
it on load ( single unit ) . Then check the phase sequence
of DG's and then give the synchroniizing command
| Is This Answer Correct ? | 2 Yes | 4 No |
what are the shades for mimic diagram i.e for 3.3kv,6.6kv,11kv,22kv and 33kv? which is the IS for mimic diagram?
what is stator inter turn fault?
what is phase angle and how its generate moreever how we measure the phasse angle?
Why in Hv transmission line as we see there are generally 6 or more than 4 conductor wires are used instead of 4 i.e. 3 for phase and 1 for neutral wire?????
what is difference between earth and ground?/
3 Answers Sree Rayalseema Green Energy Limited SRGEL,
3 phase Motor will be given 2 phase after 2 to 5 second we given 3rd phase so Motor Run sum-time in forward or sum time run reverse direction. All time phase sequence is not change. Why motor run in reverse direction? Please Explain........
Explain the power rating of a bulb, say 60W, what if the voltage changes
Three phase star connected PT transformer primary side one phase fuse is blown what will be the output in secondary side(Secondary side also three phase star connected)
megger how much voltage will produce ?
What will happen if the interpoles in case of a generator have opposite polarities to that behind it in the direction of rotation ?
Why transformer rating in KVA? describe.
What is the reason for using a GE G101 MCB in place of an EP102 MCB if both are capable of AC circuit protection?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)