how to syncronize two dg sets
Answers were Sorted based on User's Feedback
Answer / shri..
1) first start the both DG set.
2) Then check Phase sequence R,Y,B
3) check the LL voltage & LN voltage. (both DG voltage
should same)
4) Check The engine RPM (both engine RPM should same)
5) Check The Frequency (both DG Frequency should same)
6) Then close the both breaker.
7) then cross check the voltage,Frequency,RPM
Is This Answer Correct ? | 9 Yes | 1 No |
Answer / santhosh
DG Sets with equal Voltage, Frequence and RPM should be
connected to a single bus with equal polarity and phase
sequence. Both the DG's should be protected with protecting
devices like breakers.
DG's should be operated in such a way that is starting only
one DG should get ON and as the load crosses 75% of the
capacity of DG then the second DG should get ON.
This will help in minimisng the consumption of fuel, Load
sharing and improves the performance of DG.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / satender
you have first of all Start stop the DG's in manual mode ,
then check the voltage biasing and speed biasing by running
it on load ( single unit ) . Then check the phase sequence
of DG's and then give the synchroniizing command
Is This Answer Correct ? | 2 Yes | 4 No |
what is LOS(line of sight)?
if we have a power factor 0.99 and we add a capacitive bank with it then what happen?
What is PF? Formula for calculating PF in HT side?
HOW MANY POLES ARE THERE IN 3 SLOTS PER POLE PER PHASE MOTOR
what is reactive power?, why its measured in VA ? is it transient behavior of system?
how many voltage or current enough to kill a person?
The power consumption, in case of centrifugal loads (like pump, fan, blower etc.), proportional to ____.
what is the relation between Sq mm of wire and its current carrying capacity?
A simple Question from all.... If Voltage drops then its rated value what will be effect on a Residential load? similarly if voltage rises from its rated value then what will be effects on a load? i know if voltage drops the equipment or device draws more current then its rated what are other reasons ? thanks in advance for ur time.......
what is mean by dry frequency
what is reactive and active power?why we need power factor correction?
What it the purpose of parallel phasing transfomers??
0 Answers Asia MotorWorks AMW,