Answer / santosh kumar jha
BDV means break down voltage.
This is the test of di-electric strength of transformer oil.
The sample is taken in electrolysis pot and applied a
voltage diff between anode and cathode of the pot , the
diff between the two plate is 2.5 mm.At first we appling
the voltage diff gradually , the voltage near which the oil
looses its insulation property, that voltage is called BDV.
| Is This Answer Correct ? | 157 Yes | 7 No |
Answer / ilononurb
we can take the break down voltage of transformer oil by
using oil tester. Take oil sample of tr oil and put in to
the testing oil pot with the spere electrode of 2.5mm gap.
Applied gradually the voltage till the oil losses its
dielectric stenght. breakdown voltage will display to the
oiltester meter. As per IEC 156 Standards it should be
40kv.eff.
| Is This Answer Correct ? | 78 Yes | 8 No |
Answer / rahul sharma
BDV tests is used to test the dielectric strength of the
transformer.
A new transformer oil shol\uld have at least dielectric
strength of 39 KV as per british standards.
Transformer oil used are normally tested using ASTM D877-82
with the KV strength testing,using 1" electrode spaces 0.1"
apart & test voltage increased at 3000 volts\min until it
breaks down. The avg KV obtained after 8 trails is
considered the oil dielectric strength.
Using this test dielectric strength at 30KV & above is
considered good. Dielectric strength between 23 to 29 KV is
considered usable ,but requires filtering, below 23 KV
transformer oil should be replaced.
| Is This Answer Correct ? | 41 Yes | 8 No |
On TRANSFORMER OIL BREAK DOWN VOLTAGE test is carried out which is done on field while filling the oil in transformer. This process is also called oil filtration.
1.Take sample from top of Transformer before filtration.
2.The BDV of oil should withstood min 50 KV
3.The gap between the test electrodes sample to be 2.5mm maintained
4.At least 5 sample(top/bottom) should be checked separately while filtration.
5. The samples should withstand 50 kv for 1 min.
5. Take the average of all the samples timings.You will get value.
7.Procedure
a.Voltage should be gradually increased from 0.
b. At one point Flash will take place and that point is
termed as Bread down Voltage
| Is This Answer Correct ? | 26 Yes | 4 No |
Answer / s.anand
take sample before maintank bottom this coreact methode
| Is This Answer Correct ? | 2 Yes | 1 No |
what is the difference between the megger and multimeter operation ?
what is fault level of power system ?
In 3.5X150 Sq.mm cable what does 150 stand for outer dia or inner dia?
what are the industrail measures to overcome ferranti effect? how would the ferranti effect the power system if those remedial mearsure arent taken? how often does this effect occurs in real power system? plz reply
salam, hi, how to calculate british temperature unit (B.T.U)?
why the emf of a cell more than the terminal voltage when the cell is delivering current?
What shocks us , Current or voltage?
How can two 3 phase transformers of same KVA and Voltage be connected in parallel?
0 Answers Bernhard Schulte Shipmanagement,
why rating of motor in HP?
If we have a 2000kva load,How much kvar capacitors we go to add to improve the power factor at 0.9?pls give the calculation and fully theory?
advantage of cu cable over al cable
Power systems
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)