What is the difference between bushing and insulators.?
what is the creepage distance?
Answers were Sorted based on User's Feedback
Answer / avd
Bushing : It has two parts 1. A hollow insulator may be
filled with oil or air depending on type 2. A conducting
stud or bus bar. Bushing is used to take out/in the power
from a machine without touching the ground parts.
Insulator : It is solid insulated material to isolate one
end (Live) to other end (Ground).
Creepage distance : Just imagine you have one insulator. An
ant starts from one end of insulator to the other end of
insulator. It has to travell on surface of petticoats also.
Distance travelled by ant is the creepage distance.
Hope this will clear your query.
Is This Answer Correct ? | 41 Yes | 5 No |
Bushing is used in transformer ,in ct/pt,in ht panel.
Insulator used in over head lines
creepage distance is the distance between two conductors it
should be 1200 mm.
Is This Answer Correct ? | 12 Yes | 13 No |
Answer / titeuf
help pleeez ... What is the différence between Oil to air
bushings and oil to oil , Oil to SF6 ?
Is This Answer Correct ? | 3 Yes | 6 No |
Answer / gunasekaran
bushing also one type of insulator bushing is using for higher voltage application for big transformer we r using condenser bushing bushing it is oil filled insulator there is no oil
creepage distance is distance b/w 2 conducting part along the suface of the insulator for low poluted area 16kv/mm
for moderated 20kv/mm for heavily poluted area 22kv/mm
for industrial 25kv/mm
Is This Answer Correct ? | 5 Yes | 14 No |
Why we choose 400kv,220kv,132kv,66kv,33kv transmission voltages for transmitting power. Why not other voltage levels.
21 Answers College School Exams Tests, HC, HCL, Jaypee, JPMorgan Chase,
What is the basis for selecting Vk/2 or Vk/4 for REF and Differential protection of Transformer and What is the significance of magnetising current
WHAT IS FAULT CAPACITY OF HT MOTOR TERMINAL BLOCK? ANY BODY HAVE ANSWER PLZ....POST IT.
what is the difference between KW and KWh?
why voltage between neutral and earth, with out secondary grounded distribution transformer
difference between a diode and thyristor?
how to calculation increase capacitor,increase power factor for three phase.
a battery is having capacity 100AH and 25% charging .if a load taking 10A & connected 6 hour .what is the final condition of the battery.
what should be the no load current for 3 phase ac motors ranging from 5 kw to 1000kw?
Whot is the braking capacity for MCCB. How we select different braking capacity.
What is the method for testing the differential protection stabilty in generator? When the time of starting What will happen if differentail protection connection wrong means?
How to calculate the Sizes of the cable required for one specific load? Is there any formula for that? ( EX: For 400KW load,50mtr Length, What is the LT cable Size required?)