What is Square Root Extractor for?
Answers were Sorted based on User's Feedback
Answer / shahzad
square root extractor is using for flow measurement
| Is This Answer Correct ? | 98 Yes | 11 No |
Answer / touch2gobi
Shahzad said only light answer....
We can’t measure the flow value directly.
First crate diff pressure in flow line using orifice,
annular pipe, venturi meter etc…
Then measure the diff pressure using any diff pressure
transmitter take square root get flow value.
Flow value = Sq.Root (Diff Pressure)
Any Comments, Please welcome (touch2gobi@yahoo.co.in)
| Is This Answer Correct ? | 59 Yes | 8 No |
Answer / leigh
In a differential pressure flow meter (orifice + DP Cell), pressure is measured before the orifice and after it. This pressure difference is used to measure the flow of the liquid in the pipe. If the pressure difference is more, the flow is more and vice a versa. The problem with this method is that the pressure difference is not proportional to the flow so if the velocity (flow) of the liquid increases, the pressure increases but at a different rate. If you were to plot this on a graph you would get a curve. This curve is not much good for auto control requirements. We have to make this curve straight or linear so that we can get a linear signal from the meter. A square root extractor is used to do this.
| Is This Answer Correct ? | 33 Yes | 2 No |
Answer / s. kanniyappan
Square Root extractor are used in Flow measurement in pipe
lines of low slurry and low viscous fluids by using Orifice,
Venturi, Annubar...
flow is measured by creating differential pressure along
those devices and taking square root extraction in either
transmitter side or in controller side.
some of the flow measurement devices like cariolis mass flow
meter, magnetic, vortex etc... which measure slurry and
highly viscous materials does not have square root extractor...
| Is This Answer Correct ? | 26 Yes | 9 No |
Answer / hasrat ali
normally,output of the flow transmitter will be in square
root scale, where the control valve opreate into a linear
scale.In order to change the square root output into a
linear scale we interdouce square root extractor which will
give the linear output to opreate the final control element.
| Is This Answer Correct ? | 15 Yes | 1 No |
Answer / umar khayam
The relation between the differential pressure and the flow
is not leaner.the square root is used to linerize this
relation.u can calculate the flow of a dp flow transmitter
in % by using this simple formula (flow in %= 10(under root
of delta pressure in %)
| Is This Answer Correct ? | 16 Yes | 6 No |
Answer / nishat
flow is directionally proportionalto suare root of differencitial pressure
f=square root(p1 - p2)
so suare root extractor is used to solve the square root so that we could get correct flow
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / ehtsam talat
DP & flow relation is non linear that is why square root is
used.it actually makes this relationship linear.
Q=10 under root Dp
Q=flow is %
| Is This Answer Correct ? | 8 Yes | 8 No |
Answer / dharmendra bhagwagar
The pressure differential over a distance represents potential energy (like a voltage), and the kinetic energy of the flow is proportional to the square of the mean velocity of the flow
Reference https://www.physicsforums.com/threads/i-need-an-easy-explanation-for-a-flow-formula.121914/
Reference https://www.physicsforums.com/threads/i-need-an-easy-explanation-for-a-flow-formula.121914/
| Is This Answer Correct ? | 0 Yes | 0 No |
define feed forward control loop with example and drawing?
Can any body help to get Rsemulator 5000 free from internet if possible then give me any link or any help .
what is positive displacement meter.
A motor is taking 15 Amps at no load and 60 Amps at full load. and a valve has to open 10% at full load and 80% at no load. How to draw ladder logic.(PLC).
What are different types of orifice plates? State their uses.
how to calibrate load cell
How will you test a transistor with a multimeter?
HOW TO SOLVE PROBLEM WITH ENRAF LEVEL TRANSMITTER 854 ATG THAT PASSWARD DO NOT Exist INTO TRANSMITTER TO ADJUST LEVEL WITH PORTABLE PET 847, WRITTEN WRONG PASSWORD , I AM SURE THAT DEFAULT PASSWARD (W2=ENRAF2) IS THIS TRANSMITTER NEED TO REPLACE SOFTWARE AND HOW?
why we use sensing type(NPN)on a vibration monitring system not a (PNP)sensing type
dear sir we have insatlled positioner model no.sipart PS2 make Siemens at our control valves . now problem is if we want to increase the response of valve opening speedy /fast. what parameters do we change for positioner ? any idea. please guide us.
how do we commission inergen system?
Can we used Condensate Pot on flow transmitter which is using on liquid having sluge and DP transmitter is in pit and below the process line,Can we used Condensate pot for accamulate the Sluge?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)