Bigger size actuator are required whenever thrust required
for control valve is higher. Thrust required is higher
whenver control valve has to open against high differntial
pressure. Also whenver type of packing is Graphite , large
size actuators are required because packing friction is
higher compared to PTFE.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / ku
Normally the selection of the actuator is governed by the
maximum dp shutoff for any service, You have find out what
could be maximum possible inlet pressure to the control
valve and minimum possible downstream pressure, which will
provide you maximum delta P that your actuator should
handle, for example you have a column operating at pressure
P1 and a pump is taking suctionfrom this column and the
control valve is at outlet of the pump, the pump is
discharging this material to a drum with certain pressure,
in this case you will take the shutoff pressure of the pump
as inlet pressure and minimum pressure that can be at the
drum. This will automatically result in an actuator sizing
and selection suitable for this service. I am not sure why
you mentioned bigger size actuator as actuator should
be "big enough" to handle the maximum delta P across the
control valve.
| Is This Answer Correct ? | 3 Yes | 0 No |
for high pressure application we use the the bigger actuator is wrong concept, mostly in the early days days we used this kind of actuator, mostly used for diaphragm and piston type actuator , if u use diaphragm type then u need big cascade, for high pressure , but we should change the cascade for regular intervel. in our company we control the 220 kg/cm2 of pressure in the small actuator only, bigger actuator is disturbance only large space is needed and difficult to calibrate. thanks
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / rahul
when valve size is more,
mostely for control valve
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / joby
if the valve is in higher size ,we have to go for higher
actuators for operating the valve.
FOR ESD VALVES
if the valve size is more than 18" mostly the suppliers
prefer hydraulic systems for operating the actuator
instead of air.The pressure required to operate the higher
size actuator will not be sufficient ,if you are using
plant air.
| Is This Answer Correct ? | 1 Yes | 3 No |
Foe selecting control valve if i have the min,normal & max data of flow rate,inlet pressure& outlet pressure,inlet tem.&density than how can i assure that these data are correct,pl. let me know if therew there is any method to check it.& also how we assure that the Cv we get from this data is suitable for valve for controlling require flow.
diff bw range and span?
I want to use 1/2 inch SS316 tube in my high pressure & temperature (64 kg/cm2 & 500 deg C)after condensate pot in pressure tranmistter. 1) Is it possible to use 1/2" ss316 tube in high pressure and temperature line. Tube manufacturer is local vendor. 2)On sarting the plant, We need to do system fluse that time condesate is not in the condesate pot so steam is directly contact with the tube. We have no exact calculation to know our tube is ok or nor at this time. pleae,reply.
How to define the size of control valve?
I m appointed as an automation trainee engineer in small firm in that I am only the one , my company give me a project on s7-200 as i m beginner I don't know how to program so please send me the helpful site so that I complete my project before deadline....please help me out in this critical situation.
Can anybody tell which type of quections are asked in interview for projects? plz give its urgent.....!
WHAT IS AN INTERLOCK SYSTEM ?? HOW THEY WORKs ?? WHERE IT IS USED ??? MAINLY ??
2 Answers TATA, Tata Steel Limited,
what is the difference between transmitter and converters?
what is reset windup in integral control?
if my 6 kva UPS gives 20 min. backup at 100 % load, then at 25% load what is the backup time?
what is working principle of vibration prob
what is the meaning of potential free contact. difference between dry and wet contact?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)