why we use by pas on a positioner? When can a by pass be
not used on a positioner ?
Pneumatic positioners equipped with a bypass option can be removed for maintenance without interrupting the valve service.
A position bypass is/was a common optional feature on pneumatic positioners that receive a pneumatic control signal (typically 3-15 psi, 20-100 kPa, or 0.2 - 1.0 bar) from a controller or I/P.
The bypass option is a pneumatic switch. The inlet is the control signal. The valve's outlet is either the positioner (normal mode) or the actuator (bypass mode).
If the positioner needs servicing, the bypass switch is changed from normal mode to bypass mode and the control signal will drive the valve actuator directly. The bypass assembly can typically be removed from the positioner with a couple bolts so that the bypass assembly remains connected to the process, while the positioner is removed for service.
Positioner Bypass operation does not work
- on valves with actuators whose input signal range does not match control signal range (a 1:1 output:input signal ratio). A valve actuator that requires 40-60 psi to actuate will not be actuated by a 3-15psi control signal.
- for split range valves
- for valves with control action (direct or reverse) the opposite of the control signal action.
- Electropneumatic positioners that use a 4-20mA input signal have no bypass option because there's no pneumatic signal to bypass to the actuator.
Carl Ellis
Measure First
| Is This Answer Correct ? | 1 Yes | 0 No |
what is the reason while warning lamp is on while the engine is cranking?
Can u tell me the principle of the tc,rtd,level switch,pressure switch ,transmitter(pr flow level temp.),vibration...plz
Lube oil pressure transmitter local it's showing 9.8 kg/cm2 but dcs side it's showing 9.26 like that what is the reason?
how can we calibate ph meter. how can we calibrat conductivimeter how can we calibrat massflowmeter & it s working.
What is Erosion in a control valve?
what is remote mount with MTA option? (In case of Dual Sensor Vortex Flowmeter,rosemount has written in its catalog drawings).
what is orfics working in main steam line. is it increase pressure, velocity of steam flow and dicrease steam flow rate. or any other
What is the role of P(Protional), I(Integral) and D (Derivative) in PID Controller?
in which principle pressure tx,level tx ,flow tx,temp tx ,control valve works?
Control valve question what is the meaning of cauge.?what is the use of cauge?
How to do manual mapping in radar type level transmitter?
which gas or which liquid is filled in capillary of dial type temperature indicators on power transformers
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)