why we use by pas on a positioner? When can a by pass be
not used on a positioner ?
Pneumatic positioners equipped with a bypass option can be removed for maintenance without interrupting the valve service.
A position bypass is/was a common optional feature on pneumatic positioners that receive a pneumatic control signal (typically 3-15 psi, 20-100 kPa, or 0.2 - 1.0 bar) from a controller or I/P.
The bypass option is a pneumatic switch. The inlet is the control signal. The valve's outlet is either the positioner (normal mode) or the actuator (bypass mode).
If the positioner needs servicing, the bypass switch is changed from normal mode to bypass mode and the control signal will drive the valve actuator directly. The bypass assembly can typically be removed from the positioner with a couple bolts so that the bypass assembly remains connected to the process, while the positioner is removed for service.
Positioner Bypass operation does not work
- on valves with actuators whose input signal range does not match control signal range (a 1:1 output:input signal ratio). A valve actuator that requires 40-60 psi to actuate will not be actuated by a 3-15psi control signal.
- for split range valves
- for valves with control action (direct or reverse) the opposite of the control signal action.
- Electropneumatic positioners that use a 4-20mA input signal have no bypass option because there's no pneumatic signal to bypass to the actuator.
Carl Ellis
Measure First
| Is This Answer Correct ? | 1 Yes | 0 No |
What is the SCAN time of a DCS/PLC? What is the typical value for scan time of DCS and PLC?
6 Answers Essar, Gasco, Siemens,
What is mean by analytical instrumentation?
FOR CO/CO2/O2/NOX applications which of the following manufature is best? and what is the basic principle of gas analysers? ABB/YOKOGAWA/EMERSON/SIEMENS/TELEDYNE/THERMOFISHER
WHAT IS THE DIFFERENCE BETWEEN PLC AND DCS
55 Answers ABB, Adani, Adani Power, GMR, IIUC,
what are the three main programming languages in plc
plc trouble shootings?
You wish to SINK all my digital inputs to a PLC digital input card. Would you common out the leads to a positive or a negative connection?
modbus and profibus communication difference?
what is modbus & what signals are taken through it
Can any body help me,The GE Mark V control system is windows based or Dos based?
what is the formula for changing Range of Transmitter from X mmwc to some Y mmwc with respect to DCS NCMH flow range from x NCMH to y NCMH?
What is full form of hart communicator?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)