why we use by pas on a positioner? When can a by pass be
not used on a positioner ?
Pneumatic positioners equipped with a bypass option can be removed for maintenance without interrupting the valve service.
A position bypass is/was a common optional feature on pneumatic positioners that receive a pneumatic control signal (typically 3-15 psi, 20-100 kPa, or 0.2 - 1.0 bar) from a controller or I/P.
The bypass option is a pneumatic switch. The inlet is the control signal. The valve's outlet is either the positioner (normal mode) or the actuator (bypass mode).
If the positioner needs servicing, the bypass switch is changed from normal mode to bypass mode and the control signal will drive the valve actuator directly. The bypass assembly can typically be removed from the positioner with a couple bolts so that the bypass assembly remains connected to the process, while the positioner is removed for service.
Positioner Bypass operation does not work
- on valves with actuators whose input signal range does not match control signal range (a 1:1 output:input signal ratio). A valve actuator that requires 40-60 psi to actuate will not be actuated by a 3-15psi control signal.
- for split range valves
- for valves with control action (direct or reverse) the opposite of the control signal action.
- Electropneumatic positioners that use a 4-20mA input signal have no bypass option because there's no pneumatic signal to bypass to the actuator.
Carl Ellis
Measure First
| Is This Answer Correct ? | 1 Yes | 0 No |
I want measure the volumetric flow of gas in waste heat recovery Boiler?Tell me how and which type of instruments required. Plz mail me:naba02222@gmail.com Sam please post the answer .
what is IPS (instrument protective system)?
What is the use of temprature compensation?
Can please tell mi about SIOS, PRM, SERVER, and what is the diference between PIN LAN, PCS LAN,APC Server, and please send the Doc if possible for referance,mail id patil_amit17@yahoo.com
what is the difference between auto tuning and manual tuning of controllers(eg:PID,PI,PD CONTROLLERS )
how can use ram
What should be the ideal tapping location for pressure differential transmitter for liquid service. If the tapping taken from the top of the pipe then PDIT will work properly or not. If PDIT do not work properly then what minimum corrective action should be taken in order to solve wrong tapping locations.
what is the criteria to decide conductor size of a cable ?
Can combine control system for Emergency control system (ESD)and Fire & Gas System ( F & G) is possble to built and offer to client? Can such system is as per Norms in India?
Can we use PLC in Hazardous Area?
How many types of sensor
what is difference between accelerometer vibration sensor and proximity vibration sensor
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)