The hardware electronic controller you are using has a 1-5
Volt input but the transmitter you use in the field, is a 4
to 20 mA transmitter. So in order for the hardware
controller to accept this input, you install a 250 Ohm
resistor on the controller's input which will convert it to
a 4 to 20mA input.
Weather you need a I/P converter on the control valve
depends on the positioner you will use. The hardware
electronic controller will give a 4 to 20mA signal to the
control valve, so if you want to use a full pneumatic
positioner on the valve, you need to install a I/P converter
and calibrate it for a 4 to 20mA input and a 20 to 100 Kpa
pressure output. You then need to calibrate the pneumatic
positioner for a 20 to 100 Kpa = 0 to 100% stroke.
If you want to use any other type of positioner a I/P will
not be necessary, since in electromechanical positioners the
I/P is already part of the positioner and obviously in SMART
positioners, the input to the positioner is 4 to 20 mA.
Good luck
| Is This Answer Correct ? | 24 Yes | 2 No |
Answer / vishal sharma
we need 250 ohm resistane because when we need to opearte
any loop eg.line pressure control loop er need to instal
pressure transmitter in line after control valve on that
time if we instal 250 ohm resistane in controller we dont
have to need another SMPS install for 24v signl to pressure
trasmitter for 2-wire system after install 250 ohm
resistance we recive 24v output trrough controller.
| Is This Answer Correct ? | 0 Yes | 4 No |
Answer / rohit
A electronics controller needs 4-20mA current and we have
230v or more voltage in industry so to maintain flow of
current 250 ohm resistance is vital.
I=V/R
| Is This Answer Correct ? | 2 Yes | 16 No |
what is differences between singal acting and double action valve
1 Answers Carlo Gavazzi, Welspun,
how to use K thermocouple instead E- type without compesation cable
i want to make project on process control using plc.please give me idea about this.
how many pulses are required by a ac induction servo motor of 4 poles with 50 Hz frequency to rotate by 1 degree?
HOW TO CHECK THERMOCOUPLE AND RTD & WHAT IS THE DIFFERENCE BETWEEN THERMOCOUPLE AND RTD
what is the difference between two wire transmitter and 4- wire transmitter
What is the standard height for stancion supports?
hye SAM acn u send your e mail id, so that i can solve my query through e mail?
which types of oxygen analyzer describe with drawing ?
what is sinking and sourcing....
what is the significance of hook up
Can be operate control valve without positioning if yes ? how and why?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)