IN OLTC we observed "OUT OF STEP" Alarm, we have two
different transformer, when both are in parallel this type
of alarm observed. what's the meaning of this alarm and why
it occurs???
Answers were Sorted based on User's Feedback
Answer / nasseem
Out of step means that the Two transformers at different tap.
i.e. TR-1 at tap n and TR-2 at tap n+1 or n-1.
And as you know the two transformers should have same tap
"if the two transformers have same tap size i.e 1.25% for
example" when it operated in parallel to prevent the
circulation current between the two transformers.
So it seems in your case if we assume TR-1 is master and
TR-2 is follower TR-1 change its tap position while TR-2
still at it is original tap.
Is This Answer Correct ? | 13 Yes | 0 No |
Answer / karthik
For details of the parallel operation of transformer refer
the website:
http://nptel.iitm.ac.in/courses/IIT-MADRAS/Electrical_Machines_I/pdfs/1_14.pdf
According to the literature the cause for the out of step
operation maybe due to
1)Change in voltage ratio
2)Change of polarity
Is This Answer Correct ? | 3 Yes | 2 No |
Answer / arun kumar
Out step alrm occurs when the tap changer goes to maximum /
minum tap position
Is This Answer Correct ? | 3 Yes | 9 No |
what is the harmonics? which harmonics(fundamental and reference) is suitable for calculating capacitor bank and Active filter and passive filter? what is the 1st 2nd 3rd 4th 5th harmonics and effects?
why we change the direction of winding in rotor ?how we make the north and south pole?
they conducted technica for 1 hour..i also managed..they selected 5 boys and only one girl,myself got wait listed.whether they would call or not
How many 2 ton window A/c can runs on a 125 KVA generator?
what is the size of trasmission conducatar
What is the use of conservater, bucchos relay, breather in a transformer?
8 Answers Bosch, Wipro, Zadco,
Why the power generated in dams is complex power? Why the generators in dams cannot produce Real power directly (i.e power which has zero reactive part)?
why we used to transmitt the power at higher voltage why not at lower voltage
what is phase to phase fault? what is line to line fault?
What is maximum power transfer theorem?
what is acceptance test in electrical engineering.
why ct mensioned 0.5/5p20 plese any reply to me