If an induction motor is restarted before its rotor stop
rotating, then what will be the amount of current drawn?
Is this current will be the same as motor starting current?
Answers were Sorted based on User's Feedback
induction motor takes less currunet compare that of
starting current.why because the
rotor is in running condition,(ie back emf of rotor is
'not equal to 0') "Back emf have some value while rotor is
running, so the motor takes less current compare than
starting current"
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / savan patel
IT WILL DRAW MORE CURRENT THAN MAXIMUM SPEED AND LESS
CURRENT THAN STARTING.
| Is This Answer Correct ? | 8 Yes | 2 No |
Answer / lova subrahmanyam
in induction motor starting current is 3 times more than the
full load current at the time of starting.why because the
rotor is in stand still condition,(ie back emf of rotor is
'0').that's why to induce the emf in the rotor it takes more
current to produce the torque.onece the motor reaches the
rated speed it will take normal load current.if u cut off
the suupply
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / k.prakashchandra
Less current,as the moment of inertia is zero
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / akash kumar
I=Vs/(Sqroot(Sqr(R/S)=Sqr(X)))
R= stand still resistance
X= stand still reactanc
s= Slip
if u still have the slip.....it will b according to slip only
| Is This Answer Correct ? | 0 Yes | 0 No |
how much winding resistance of 0.75kw to 12.5kw 3ph sqwiralcage induction motor?
How to decide the input and output circuit breaker for a 1600kva transformer.Is there any calculation is involved.
please suggest some good universities with low cost iam in totally full confusion so please help me my profile gre 283 and ielts 5.5
A 100 kVA , 400 v/250 kv testing transformer has 8% leakage reactance and resistance on 100 KVA base . A cable has to be tested at 500 kv using the above transformer as a resonant transformer at 50 hz . if the charging current of the cable at 500 kv is 0.4 A find the series inductance required . Assume 2% resistance for the inductor to be used and the connecting leads . Neglect dielectric loss of hte cable . what will be the input voltage to the transformer ?
What are the various reasons for an inductin motor to get heated?
If the capacitor bank is installed in switchyard say 132/22kv then on LT side say 22kv/0.433kv is it necessary to install capacitor bank for maintaining power factor. if pf is maintained on HT side then will that be maintained on LT side as well.if not then how&why??????/ please explain...........
What is the procedure/activities to be taken to inject the current more than 2000A by using 2000A Loading Transformer?
why the rotor current becomes in steady state during high slip region? please verify with equations.
if There is Short circuit in Power Transformer, what will happened to Buchholz Relay.?? How Buchholz Relay will respond.??
Why 4 pole generator generates more power and 6 pole generates less power campare to 4 pole
2 Answers Julius Berger, Suzlon,
stand by earth fault protection (51G) for transformer rating 2000 kVA,Dyn11,33/0.400 V. LV NCT ratio and necessary resistor and metrosil values how to calculate
where we use 1 phase & 3 phase supply ?what is major advantage using 3 phase over than single phase ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)