Explain how you can give the overload setting to any Motor
Protection
Relay for a HT motors with formula and example?
Answers were Sorted based on User's Feedback
Motor current rating is calculated by using the formula
I= P/1.73*V*PF
Normany it is 1.8times of power of the motor will be their
in 420v 3 phase motor.
Ex: 500Kv HT motor 11kv voltage
is Approx. 32A is the rated current.
so 32.5 or 33A is OL Setting.
| Is This Answer Correct ? | 6 Yes | 3 No |
what percentage of marks in B-TECH is needed for section engineering exam
1 ton AC takes how much current( starting & stable)
what is the setting of locked rotor in HT motor ? (answer expecting in percentage)
what is the ambient temperature of transformer oil & winding?
Why CT secondary should not left open??????????
can we start mulitple 3 phase induction motors with common starter?
Can I use less voltage cable for neutral, since the voltage of return path is zero ideally?
how to protect motor in dol starter having capacity of 30 hp.40 hp?
Energy metering: On the property I am renting, the supply voltage is 2 x 110 volts. These 2 x phases enter a energy meter which then exit the meter to over head lines to my house. Question 1. The meter is single phase 240 volts but is being used as 2 x phase(2 x 110volt), is this acceptable? if not, please give me the reasons. The meter details are as follows: 60Hz 15amp Imax 100 amp Kd 3,6 Wh/R 1 fase 3 hilos Model FX 231. I think it was manufactured in Brasil From this meter, the cables run along over head aluminum conductors,I estimate the cross sectional area to be 25mm diameter, but the neutral is only about 10mm square diameter, which cover a distance of 170 meters and then terminate with an underground cable of 65 meter length, total length = 235 meters. There must be a huge voltage drop over this length. This line is protected with 2 x 200 amp aluminum fuses after the meter, there is no main switch in the distribution board. These 2 phases connect directly onto 2 busbars. Surely the neutral should be the same size as the conductors if not more? Question2. What are your thoughts about this installation, should there be better protection, is the neutral too small? During the night, the lights dim then brighten all the time, this cannot be good for my electrical appliances. In my home, I only have a small electric geyser and fridge, my stove works off gas. But when i use other appliances like the washing machine or microwave oven, the light dim. The internal wiring of this house is done with solid hard drawn copper wires and of course, they have to be under rated. I am a retired electrician by trade, but not on the metering and over head mains side, my experience is on the factory maintenance side of things. Your expertise on these matters will be greatly appreciated. Please inform me how to rectify or make any improvements Kind regards, my power bill is very expensive, so I need to know how to bring it lower. Kind regards, Brian
what is mean by hormonics & surge? and it's effects?
Is any AC drive(VFD) had a feature of DC injection braking? if available please mention the detail. i.e drive can supply braking torque when the motor in idle state.
what is the difference between direct loading and indirect loading?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)