Answer / vinod g
In Restricted earth fault protection Three phase CT is
parralleling (shorting all S1 andshorting all S2 together)
and paralleel conection with Neutral Relay and CT. IN
Healthy conditon current in all the three phase will be
balanced and summation will be zero. During earth fault out
side CT area summation of phase CT currents and Neutral CT
zero, so relay will not pick up. When earth fault inside
the transformer the current in the CT will differ and Relay
will pick and trip the tranformer breaker,so it is clear
that REF is for Transformer Winding protection and Bushing
CT is normally using for phase CT
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / pintu
THIS IS CALLED 5 CT CONFIGURATION (3 PH. CT + 1 X'MER NCT +
1 BB N CT)OF REF PROTECTION. ALL THESE FIVE CTS ARE TO BE
CONNECTED IN PARALLEL. TRANSFORMER NCT SHOULD BE LOCATED
AFTER NEUTRAL BIFERCATION (I.E. PATH TOWARDS EARTH) AS THIS
IS DEDICTAED FOR DETECTING THE RESIDUAL CURRENT IN CASE OF
GROUND FAULT. BUT NEUTRAL BUSBAR CT IS NOT FOR DETECTING
THE FAULT CUURENT BUT FOR THE UNBALANCE CURRENT IN THE
SYSTEM. IT SHOULD NOT BE TRIPPED DURING THE EARTH FAULT.
IN 4 CTS CONFIGURATION OF REF PROTECTION, NEUTRAL BUSBAR CT
CONNECTION WILL NOT BE THERE. YOU SHOULD DECIDE THE 5 OR 4
CT CONFIGURATION AS PER YOUR SYSTEM DESIGN.
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / anup mahajan
The purpoae of Restricted earth fault (REF) is to provide
the protection of transformer neutral in case of residual
current. As the fault which lies near phases are known as
external faults and is to be detected by differential
protection but the residual current which is not going to
ground and circulates between neutral and phases are
detedted by REF protection. Please keep in mind that CT
characteristics of this REF must be matched with phase side
CT characteristics.
| Is This Answer Correct ? | 2 Yes | 8 No |
Synchrounous motor is three phase motor,but its not self starting .why?
23 Answers Delta Beverages, KI, L&T, NTC, TVS, Wipro,
What are objectives of energy managements ?
what is current check gurd relay?
What should be cable size for 75KVA 380/220 3ph transformer
power inverter we are using 2n3773 power transister in that places we can use any IGBT ?
For an 100kw generator, only 50kw of load is connected. Will the generator generate only 50kw or 100kw. If it generate 100kw what happens to rest of the 50kw. What happens if we connect more than 100kw of load?
What should be the overcurrent, instantaneous overcurrent, short cicuit current settings (i.e. how many times of motor full load and what is the time duration) for a motor?
why a bulb glow when connected with two end phase and neutral respectively.
How to calcute the cable size for both HT and LT please specify the formula for that Regards Chethan C
I have 30 kw motor load & i have selected 10 kvar capacitor bank for power factor improvement.my existing p.f is 0.85 & proposed p.f is 0.99 so ,is it right selection? 2 nd question how to connect c.bank whether in delta or star connection & how to decide it?
why are we maintaining some specific gravity in battery ?
The capacitive reactance of a capacitor of 1/(2(PI)) F at 10^3 H is
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)