Answer / vinod g
In Restricted earth fault protection Three phase CT is
parralleling (shorting all S1 andshorting all S2 together)
and paralleel conection with Neutral Relay and CT. IN
Healthy conditon current in all the three phase will be
balanced and summation will be zero. During earth fault out
side CT area summation of phase CT currents and Neutral CT
zero, so relay will not pick up. When earth fault inside
the transformer the current in the CT will differ and Relay
will pick and trip the tranformer breaker,so it is clear
that REF is for Transformer Winding protection and Bushing
CT is normally using for phase CT
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / pintu
THIS IS CALLED 5 CT CONFIGURATION (3 PH. CT + 1 X'MER NCT +
1 BB N CT)OF REF PROTECTION. ALL THESE FIVE CTS ARE TO BE
CONNECTED IN PARALLEL. TRANSFORMER NCT SHOULD BE LOCATED
AFTER NEUTRAL BIFERCATION (I.E. PATH TOWARDS EARTH) AS THIS
IS DEDICTAED FOR DETECTING THE RESIDUAL CURRENT IN CASE OF
GROUND FAULT. BUT NEUTRAL BUSBAR CT IS NOT FOR DETECTING
THE FAULT CUURENT BUT FOR THE UNBALANCE CURRENT IN THE
SYSTEM. IT SHOULD NOT BE TRIPPED DURING THE EARTH FAULT.
IN 4 CTS CONFIGURATION OF REF PROTECTION, NEUTRAL BUSBAR CT
CONNECTION WILL NOT BE THERE. YOU SHOULD DECIDE THE 5 OR 4
CT CONFIGURATION AS PER YOUR SYSTEM DESIGN.
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / anup mahajan
The purpoae of Restricted earth fault (REF) is to provide
the protection of transformer neutral in case of residual
current. As the fault which lies near phases are known as
external faults and is to be detected by differential
protection but the residual current which is not going to
ground and circulates between neutral and phases are
detedted by REF protection. Please keep in mind that CT
characteristics of this REF must be matched with phase side
CT characteristics.
| Is This Answer Correct ? | 2 Yes | 8 No |
How can two 3 phase transformers of same KVA and Voltage be connected in parallel?
0 Answers Bernhard Schulte Shipmanagement,
tell me any book for current n potential trasformer with full knowledge ?
while grounding the galvenized metallic structures is it necessary to remove the galvenization at the point of contact? Or other wise is the galvenizatio a good conductor?
how to calculate the size of cable tray
i have 6oo kva dry type transformer and its neutral is not grounded even body of transformer ground i want to know it is safe or not ?
Name a govt approved university which have 100% online engineering course.
hello... i am preparing for GET. please send me previous papers..
Why is it prefer to initiate circuit breaker failure by "86" lockout relay not by "94" tripping relay ?!
What is transformer saturation?
when it is possible kvrah lead & fundamental kwh be equal in electonic trivector meters (3 ph)
1. Design a counter which counts 0, 4, 8, 2, 6, and repeats using: 1.a using JK flip flops 1.b using T flip flops 1.c using D flip flops
All the voltage drops and the source voltage added together in a series circuit is equal to
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)