i am working in thermal power plant .
if temperature transmitter is not showing reading in dcs
then how can we rectify the problem?

Answers were Sorted based on User's Feedback



i am working in thermal power plant . if temperature transmitter is not showing reading in dcs th..

Answer / k.sreenivasan

Go to the field and check the local indication in the
transmitter.(normally it is in either engg. units or as
percentage)
If it is zero ,then the problem is in the sensor or
terminal connection, because most of the current generation
transmitters are highly accurate and have longer stability
periods.
Suppose local reading is ok,then check the DCS analog input
card for any fault condition and clear it.Normally this
situation is rare.

Is This Answer Correct ?    24 Yes 1 No

i am working in thermal power plant . if temperature transmitter is not showing reading in dcs th..

Answer / s. kanniyappan

Check the Sensor properly. if it is ok, then
1)check continuity between the sensor cables
2)tight the cables properly
3)check the transmitter supply (24vdc)
if it is not ok, then check the DCS analog i/p cord.

Is This Answer Correct ?    14 Yes 0 No

i am working in thermal power plant . if temperature transmitter is not showing reading in dcs th..

Answer / k.manikanta naidu

check the millivolts output of thermocouple.then multiply
with the standard values depends on the type of
thermocouple.if the value is ok,check the temparature
trnsmitter,then check the mA o/p of TT.

Is This Answer Correct ?    8 Yes 0 No

i am working in thermal power plant . if temperature transmitter is not showing reading in dcs th..

Answer / g kiran kumar

1. Check the wiring at all terminal blocks at field, at
control panel and at PLC for any loose connection.
2. Check the Transmitter supply.
3. Measure the output from Transmitter.
4. Check cable continuity.
5. Finally check the configuration of TAG in the DCS (may
be someone deleated accidently).

Is This Answer Correct ?    6 Yes 0 No

i am working in thermal power plant . if temperature transmitter is not showing reading in dcs th..

Answer / satish

SEE THE FIRST ALRM CONDITION ON TRANSMITTER BECAUSE MOST
PROBABILITY IN PRIMERY ELEMENT PROBLE.

Is This Answer Correct ?    6 Yes 3 No

i am working in thermal power plant . if temperature transmitter is not showing reading in dcs th..

Answer / pradeep kumar

check the tt reading once again check the main cable (from
element resistance or mv)and also check the branch
cable(from dcs 24 v)its available the problem in dcs side
check the analog modules

Is This Answer Correct ?    1 Yes 0 No

i am working in thermal power plant . if temperature transmitter is not showing reading in dcs th..

Answer / altamash

first check the TB in marshalling cabinet then check local display in transmitter and then DCS

Is This Answer Correct ?    0 Yes 0 No

i am working in thermal power plant . if temperature transmitter is not showing reading in dcs th..

Answer / srinivas

check wiring in i/o

Is This Answer Correct ?    1 Yes 5 No

Post New Answer



More Instrumentation Interview Questions

what is intrinscily safe system and where we use?

0 Answers   DEWA,


what is consistency transmitter and describe its working?

1 Answers   Emami,


Why would an Engineer consider combining FEEDBACK and FEEDFORWARD control in some applications?

4 Answers   Jindal,


please anyone suggest me some good intools training institutes with their place and contact nos.

1 Answers   ABB, Thermax,


State some of balance principle’ advantages?

0 Answers  






How digital input and digital output 's are working in dcs

0 Answers   BBV, Indiabulls,


How to calibrate DP transmitter by using HART communicator ?

1 Answers  


Which products are available in the Mass Systemswitch and System Manager AC range?

0 Answers  


plz... clarify my answer, how to calibrate vaccum (DP)leveltransmitter,it is hart. (digital).DETAILS:(coloumn)closedtank height 2650mm,and tx range is 0-1500mmH20.

1 Answers   KNPC,


How we are blocking 40 kg or more pressure through only 6 kg instrument air in control valve 

3 Answers  


What is the working principle of oxygen analyzers(zirconium oxide type) used in CFBC boilers?

3 Answers   Bajaj, Kohinoor, Wartsila,


what is the meaning of wet leg & where is it used?

1 Answers  






Categories
  • Civil Engineering Interview Questions Civil Engineering (5074)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4444)
  • Electrical Engineering Interview Questions Electrical Engineering (16594)
  • Electronics Communications Interview Questions Electronics Communications (3915)
  • Chemical Engineering Interview Questions Chemical Engineering (1092)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (214)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (258)
  • Instrumentation Interview Questions Instrumentation (2986)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (123)
  • Power Plant Engineering Interview Questions Power Plant Engineering (170)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (0)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1377)