i am working in thermal power plant .
if temperature transmitter is not showing reading in dcs
then how can we rectify the problem?
Answers were Sorted based on User's Feedback
Answer / k.sreenivasan
Go to the field and check the local indication in the
transmitter.(normally it is in either engg. units or as
percentage)
If it is zero ,then the problem is in the sensor or
terminal connection, because most of the current generation
transmitters are highly accurate and have longer stability
periods.
Suppose local reading is ok,then check the DCS analog input
card for any fault condition and clear it.Normally this
situation is rare.
Is This Answer Correct ? | 24 Yes | 1 No |
Answer / s. kanniyappan
Check the Sensor properly. if it is ok, then
1)check continuity between the sensor cables
2)tight the cables properly
3)check the transmitter supply (24vdc)
if it is not ok, then check the DCS analog i/p cord.
Is This Answer Correct ? | 14 Yes | 0 No |
Answer / k.manikanta naidu
check the millivolts output of thermocouple.then multiply
with the standard values depends on the type of
thermocouple.if the value is ok,check the temparature
trnsmitter,then check the mA o/p of TT.
Is This Answer Correct ? | 8 Yes | 0 No |
Answer / g kiran kumar
1. Check the wiring at all terminal blocks at field, at
control panel and at PLC for any loose connection.
2. Check the Transmitter supply.
3. Measure the output from Transmitter.
4. Check cable continuity.
5. Finally check the configuration of TAG in the DCS (may
be someone deleated accidently).
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / satish
SEE THE FIRST ALRM CONDITION ON TRANSMITTER BECAUSE MOST
PROBABILITY IN PRIMERY ELEMENT PROBLE.
Is This Answer Correct ? | 6 Yes | 3 No |
Answer / pradeep kumar
check the tt reading once again check the main cable (from
element resistance or mv)and also check the branch
cable(from dcs 24 v)its available the problem in dcs side
check the analog modules
Is This Answer Correct ? | 1 Yes | 0 No |
tell me about Woodward505 Function as a point of Instrument Engineer.
what happen if i install my pressure transmitter below the elevation of pipe in natural gas service. Also support your answer
WHAT ARE THE INSTRUMENTAL DIAGRAMSOF VALVES?
0 Answers Artikal, ITC Infotech,
I have a orifice installed in plant which is design for 0~100 inH2O for 0~80MMSCFD, now due to process change the maximum flow is change to 120 MMSCFD so for this new process value what will be the DP across orifice.
what are turbo generators?
For an Instrumentation Engineer, is there any effect on Instruments of safety zones like zone0, zone1, zone2. As an instrumentation Engineer, what we have to consider or remember while working in these areas.( zones 0,1,2).
Please explain for RS 485 & RS 232 communication
What is difference between Ionization heat and bimetallic heat
Dear All can any one told me that VFD Make ABB Model ACS800-01 used for dual Source like 1.DC Source applied at terminal UDC+,UDC- 2. 3 phase 400AC,50Hz
What are the types of control valves available
what are the sensor types of vibration&speed?n what is proximity sensor?
principle of rtd