IF 5000amp current on LT 440V. then how much it will draw
amp on HT 11KV side
Answers were Sorted based on User's Feedback
Answer / prabhat ranjan
since, power will always be the same so power at LT side should be equal to HT side...
5000*440= I*11000
so.. I= 200AMP at the HT side
| Is This Answer Correct ? | 26 Yes | 1 No |
Answer / pradyumna171
the voltage ratio of HT< is 25:1 (11kv/44ov) then current ratio is inversly ie 1:25 if LT current is 5000 amp then HT current is 5000/25=200 amp. we get same answer by apply any method of calculate the current.
| Is This Answer Correct ? | 10 Yes | 2 No |
Answer / santosh soni
power is transfer for receiving end are same so all power is
transfer another side
5000*440=I*11000
I=200amp
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / guest
use your KVA formula. The va of your load is
root3 X 440 V X 5000= 3810511VA
SO AT 11KV SIDE IS
3810511/1.732 / 11000 =200 AMPS
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / shamsuzzaman
HT side 22 Amp for 11Kv Line , LT side ( 11 Kv/415 Volts ) how mouch ampere of ?
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / bharath
LT5000*440*1.732=3810400KVA
HTAMP 3810400/ 11000 =346.4amp
| Is This Answer Correct ? | 10 Yes | 8 No |
Answer / m.koteswara reddy
200A
I2= V1xI1/V2
( 440x5000)/11000=200A
| Is This Answer Correct ? | 3 Yes | 1 No |
5000/25=200amp (Receprocal ratio of voltage i.e 11000/440=25)
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / pradyumna171
the voltage of HT< is 25:1(11kv/44ov) then current is 1:25(inversely) in this case if LT is 5000amp then HT current is 5000/25=200amp. we get the same answes by apply any method to calculate the current.
| Is This Answer Correct ? | 0 Yes | 1 No |
Why there are some equipment(i.e:TV) that using 2-pin plug instead of three? What happen if there is current leakage? Are we going to get electric shock??
0 Answers College School Exams Tests,
What id difference between power and energy?
What is dynamo?How it works and what is the function of dynamo in a DG.
what is meant by impedance testing of transformer and why it is used
Can anyone please provide me details of MCCB/Contactor/SFU rating calculations for a motor feeder..for example 50 kw.. not from type-2 cordination chart. i want manual calculations..
how to calculate power factor of capacitor? what is transformer rating?
which transfofrmer oil break down voltage strength get will be more if oil sample taken from bottom of tank or oil sample taken from top of the transfomer tank.
what is dry and wet frequency withstand voltage? why & where it is used??
How should i design a 1ph & 3 ph transformer. Kindly let meknow all steps and formulaes related to design from scratch.
what do you mean by star connection?
what is practical efficiency of power transformer..?
What is the difference between Isolator & Load Break Switch?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)