IF 5000amp current on LT 440V. then how much it will draw
amp on HT 11KV side
Answer Posted / pradyumna171
5000/25=200amp (Receprocal ratio of voltage i.e 11000/440=25)
Is This Answer Correct ? | 1 Yes | 0 No |
Post New Answer View All Answers
i have some screw comprressor with 630kw power,i have established them with simple star to delta circuit,by the way there is so much inertia when the screw comprressors start, can you offer me contactors power with 400vac or any cataluge to choose the contactors
What is core CT & it's function?
if two transformers are placed parallel & both have fault impedance of 50KA will it increase or decrease show example?
how cables go in and come out for distribution from the feeder pillar box?
what is difference between window type and wound type transformers?where we will use window type and wound type transformers?
How much load can take a 16 mm aluminum cable 3 phase
what is the transformer turn ratio formula and give some examples?
What are the electrical engineer roles and responsibilities in chemical plant?
Can you please explain creepage distance in detail, for a 6.6kV cable head what must the distance be and how do you determine it?
What types domain of laplace transforms? What behavior can laplace transform predict how the system work?
What is the comparison of PILC and XLPE cable
what percent do you derate your copper wire when you change from copper buss to copper wire
How to protect a Dosing pumps/any sensitive equipment (single phase) from surge protection inside a food factory.
regarding safety what would u consider the most important rules to observe when inspecting electrical equipment?
how to test the turn ratio of 3 phase transformer using volt meter shoe the curcit diagram.