IF 5000amp current on LT 440V. then how much it will draw
amp on HT 11KV side
Answer Posted / pradyumna171
the voltage ratio of HT< is 25:1 (11kv/44ov) then current ratio is inversly ie 1:25 if LT current is 5000 amp then HT current is 5000/25=200 amp. we get same answer by apply any method of calculate the current.
| Is This Answer Correct ? | 10 Yes | 2 No |
Post New Answer View All Answers
Why 30kw 40 hp 4 pole 3ph induction motor over heated?any steps on reduction in heat?
what is RNG in the DG synchronizing by PLC?
What the formula for calculating no.of earthings & size of earth strip for 100mX90m shop.
what is the meaning of 0.5ohm Resistance
how to calculate transformer turn primary & secondary side 11kv to 420v
describe the phenomena of vacuum interruption in C.B
DG cranking voltage?
What are the reasons for the parallel operation of transformers?
how to calculate units consumption for a 12 hp motor /hr.
WHATIS TIME CONSTANT? WHATIS ITS SIGNIFICANCE? ILLUSTRATE THROUGH EXAMLES.
How will you utilise electrical power? You can start from the generating station.
How to do bus bar short circuit calculation for 230KV/11kv, 60 MVA Substation?
Why Ac Systems Are Preferred Over Dc Systems?
The loads are connected with phase and ground then why current flow as the loads ?
what is feeder bay?