Dear Sir,
we met a disaster with our 62.5 kva genset, after rewinding
we informed by our contract engg that due to return current
coming in neutral & impropper earthing this happend.
But after all set up & load balance we checked & found
again we have about 20 to 32 amp return current on neutral.
we have 12 airconditioner + 12 mini fridge on single phase
line.
Pl suggest any idea to solved this problem
Answers were Sorted based on User's Feedback
Answer / guru
Ground the neutral point of Genset and your problem will be
solved
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / sheikh
I think imbalance load is main reason of this problem and cross current compensation instrument transformer should be installed on your common bus bar to prevent this loss
but balance load all of 3 phase eleminate the highest neutral current.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / rishabh sharma
i think the load on your single
phase need to be distributed to all
three phases equally. this problem
occures due to load imbalance.
| Is This Answer Correct ? | 1 Yes | 1 No |
How to use computer cpu ups use for home inverter circuit board
What is basic fundamental for choosing NGR or NGT for any generator neutral grounding
The power consumption, in case of centrifugal loads (like pump, fan, blower etc.), proportional to ____.
If we have to find the inductance of a dc shunt motor then by giving dc supply or ac supply and what is the reason for it. (this example is from "to determine the transfer function of a dc shunt motor ")
How can we calculate the rating of capacitor bank to be connected for a particular load(ex.100kw)to improve the power factor from 0.8 to 0.9?
400kw, 3.3Kv motor want to fix 1000km away from substation. What is full load current? and what is the cable size for motor? I amp expecting answer and advice from your side.. thanks...
4 Answers Kuwait Oil Company, Weatherford,
What cmos is and its benefits?
our factory is going under construction mean time transformer 1000 kva 2 nos &load break swithch 12 kv & 4 nos 750 kva 2 nos & 380 kva 2 nos generator to be errcted.how to arrange earth pits &how to earth connect & neutral pit how to calculate in earth bit size.
What is the d/f b/w MCCB & MCB
Is there any Electrical supervisor license which gives permit to work whole India rather than individual state??
For household Load of 11Kw supplying 5Nos. 1.5 ton Air conditioners + usual other load what shall be rating of Either ELCB Or ELMCB? Which of the circuit breaker will be a better choice?
How much dc volt applied in cathodic protection system?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)