Dear Sir,
we met a disaster with our 62.5 kva genset, after rewinding
we informed by our contract engg that due to return current
coming in neutral & impropper earthing this happend.
But after all set up & load balance we checked & found
again we have about 20 to 32 amp return current on neutral.
we have 12 airconditioner + 12 mini fridge on single phase
line.
Pl suggest any idea to solved this problem
Answers were Sorted based on User's Feedback
Answer / guru
Ground the neutral point of Genset and your problem will be
solved
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / sheikh
I think imbalance load is main reason of this problem and cross current compensation instrument transformer should be installed on your common bus bar to prevent this loss
but balance load all of 3 phase eleminate the highest neutral current.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / rishabh sharma
i think the load on your single
phase need to be distributed to all
three phases equally. this problem
occures due to load imbalance.
Is This Answer Correct ? | 1 Yes | 1 No |
Explain how Hormonics will effect the Electrical System?
What is the tube exial fan?
How to resolve if Diesel generator stop while running ?
Cummins 750 KVA generator how much disel consumed per hour and how many units generated on 100% full load.
what will be efficient rating of ac motor to lift a 10 kg wt of stone to 10 meter height with input 220V AC 50 Hz frequency???
What is the deference between earth fault & earth leakage
why we generally use 3.5 core cable or in other word 1/2 core for neutral and also confirm me that in balance conditiob(3 phase)current in neutral will zero
7 Answers HCIL, Jindal, Siemens,
why transmission voltages are in multiple of 11kv?
How to calculate earth flat size for 250 Kva DG and transformer?
what is ferranti effect?
can any one tell me about the Extra low voltage systems?From where we give supply to these type of systems??
if i have 5kw,9A,three phase induction motor,if i want to install it 100 meter away from its feeder,how i will culculate cable size for this load.