Dear Sir,
we met a disaster with our 62.5 kva genset, after rewinding
we informed by our contract engg that due to return current
coming in neutral & impropper earthing this happend.
But after all set up & load balance we checked & found
again we have about 20 to 32 amp return current on neutral.
we have 12 airconditioner + 12 mini fridge on single phase
line.
Pl suggest any idea to solved this problem

Answers were Sorted based on User's Feedback



Dear Sir, we met a disaster with our 62.5 kva genset, after rewinding we informed by our contract..

Answer / guru

Ground the neutral point of Genset and your problem will be
solved

Is This Answer Correct ?    5 Yes 0 No

Dear Sir, we met a disaster with our 62.5 kva genset, after rewinding we informed by our contract..

Answer / sheikh

I think imbalance load is main reason of this problem and cross current compensation instrument transformer should be installed on your common bus bar to prevent this loss
but balance load all of 3 phase eleminate the highest neutral current.

Is This Answer Correct ?    1 Yes 0 No

Dear Sir, we met a disaster with our 62.5 kva genset, after rewinding we informed by our contract..

Answer / rishabh sharma

i think the load on your single
phase need to be distributed to all
three phases equally. this problem
occures due to load imbalance.

Is This Answer Correct ?    1 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

Explain how Hormonics will effect the Electrical System?

5 Answers  


What is the tube exial fan?

0 Answers  


How to resolve if Diesel generator stop while running ?

0 Answers   Toyota,


Cummins 750 KVA generator how much disel consumed per hour and how many units generated on 100% full load.

1 Answers  


what will be efficient rating of ac motor to lift a 10 kg wt of stone to 10 meter height with input 220V AC 50 Hz frequency???

1 Answers  






What is the deference between earth fault & earth leakage

1 Answers  


why we generally use 3.5 core cable or in other word 1/2 core for neutral and also confirm me that in balance conditiob(3 phase)current in neutral will zero

7 Answers   HCIL, Jindal, Siemens,


why transmission voltages are in multiple of 11kv?

10 Answers  


How to calculate earth flat size for 250 Kva DG and transformer?

8 Answers   Deepak Fertilisers,


what is ferranti effect?

9 Answers  


can any one tell me about the Extra low voltage systems?From where we give supply to these type of systems??

0 Answers   MCB,


if i have 5kw,9A,three phase induction motor,if i want to install it 100 meter away from its feeder,how i will culculate cable size for this load.

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4452)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)