i have one absolute pressure transmitter for the range is
-400mmhg to 400mmhg. If i do the zero trim at atmosphere the
transmitter should be give 4ma or 12ma? which one is correct?
Answers were Sorted based on User's Feedback
Answer / banerjeenandan
Your transmitter has a range of 800mmhg. The LRV is -400mmhg
and URV is +400mmhg. So at atmosphere you will get 12mA. all
the time, because atmosphere is Zero gauge pressure
(perfectly mid value in between the LRV and URV).
If you do zero trim at atmosphere, it will take "ZERO" with
the atmospheric pressure. The range of the transmitter will
not change. The range will remain 800mmhg. But your LRV will
change to 0mmhg and URV will change to +800mmhg. So in that
case, without any process connection it will give 4mA.
| Is This Answer Correct ? | 25 Yes | 1 No |
Answer / senthil.doosan
-400mmhg= -0.53bar
400mmhg = +0.53bar
if u do zero trim by opening the valves with respect to atm
the output of the transmitter is 12ma
without any process connection the output is 4ma
| Is This Answer Correct ? | 7 Yes | 0 No |
Explain about the leakage class of the control valves
capillary type tranmitter using remote seals and capillary tubes filled with liquid of known of known density so if you wanna callibrate it just close block valve just before capilary @ high side & connect druck apply it's calibrated range pressure as normal calibration ensure low side block valve must be closed & if you asking commissioning so this is not a DP type pressure tx so simple if you wanna put in servie this tx just open high side block valve & than low side block same way i do it but still transmitter showing -13 ma.just tell me what i want to do ?
In control valve proximity inductive sensor is taken as digital feedback for full open and full close.Normally its volts 24v when the sensor acts the feed back voltage 14v so that our relay not indicating in plc panel . kindly give the solution.
what is the way of measuring air flow in air duct?explaim instruments used and DP creation in line?
The company where I am working, their is rosemount 5400 series radar type level transmitter, it is meant to show level of filled tank, but along with the level it is showing temperature also, so my question is how a onon-contact type radar type level transmitter can show temperature even if it does not have any contact with the fluid?
0 Answers Process Control Technologies,
Describe the functions of the Operator Interface including the considerations related to alarming and display layout/configuration/layers.
what are the values of fuel flow rate in various places in boiler.
pt range is -45 psi to 45 psi.friends can you give answer with calculation and with linerity scale like 0%,25%,50%,75%& 100%?
In most process, speed of motor controlled by control system with a reference pot . Now if i start & it becomes uncontrollable, i.e.gets directly start & stop after certain time.Then which reasons can make such problem? can motor may be faulty?how?
what is the basic working principle of I/P and Positioner in any control valve.
If any control valve create hunting problem, what is the possible reason and solution?
Is SmartPlant Instrumentation taking advantage of the quality assurance procedures within Intergraph?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)