i have one absolute pressure transmitter for the range is
-400mmhg to 400mmhg. If i do the zero trim at atmosphere the
transmitter should be give 4ma or 12ma? which one is correct?
Answers were Sorted based on User's Feedback
Answer / banerjeenandan
Your transmitter has a range of 800mmhg. The LRV is -400mmhg
and URV is +400mmhg. So at atmosphere you will get 12mA. all
the time, because atmosphere is Zero gauge pressure
(perfectly mid value in between the LRV and URV).
If you do zero trim at atmosphere, it will take "ZERO" with
the atmospheric pressure. The range of the transmitter will
not change. The range will remain 800mmhg. But your LRV will
change to 0mmhg and URV will change to +800mmhg. So in that
case, without any process connection it will give 4mA.
Is This Answer Correct ? | 25 Yes | 1 No |
Answer / senthil.doosan
-400mmhg= -0.53bar
400mmhg = +0.53bar
if u do zero trim by opening the valves with respect to atm
the output of the transmitter is 12ma
without any process connection the output is 4ma
Is This Answer Correct ? | 7 Yes | 0 No |
what is formula mv convert to temperture
IS there any effect of vortex in low pressure side of the transmiter after the orific in feed water line? if yes then what is the calculation?
what is orfics working in main steam line. is it increase pressure, velocity of steam flow and dicrease steam flow rate. or any other
What materials are used in thermo wells?
in the construction field why hook up s.s.tubing for transmitter using upto 6mtrs of closed loop, but y not open loop nomore restriction
How to do ma trim in massflow meter?
How to Calibrate Flow Switch in field
what is buoyancy law?
what is IPS (instrument protective system)?
In split range control, we will control 2 outputs with time interval. Eg :(with 4-20 ma signal, for 4-12 ma we are operating one control instrument like valve & for 12-20ma we are operating other control instrumet (other valve). If we get a signal of 15ma to first instrument (Valve 1), what will happened to the first valve, and if we get signal above 20 ma to 2 valve what will happened ?
What is exact difference between the panel earthing and system earthing in DCS system. What is the value of resistence.
when we calibrate the DP transmitter at that time which matrial we used in pressure pump?