pt range is -45 psi to 45 psi.friends can you give answer with calculation and with linerity scale like 0%,25%,50%,75%& 100%?
0 % = (-45) PSI = 4 mA
25%= (-22.5) PSI= 8 mA
50%= 0 PSI = 12 mA
75%=22.5 PSI = 16 mA
100% 45 PSI = 20 mA
Calculation :
LRV = (-45) PSI
URV = 45 PSI
SPAN = URV - LRV = 45-(-45) = 90
Calculate % of SPAN for e.g. 0 PSI is {(0-(-45))/SPAN}*100 = (45/90)*100 = 50% of SPAN
mA= [{(% of SPAN)/100}*16]+4 or in other terms ...
1% of SPAN = 4+0.16 = 4.16 mA
2% of SPAN = 4+0.32 = 4.32 mA
3% of SPAN = 4+0.48 = 4.48 mA
.
.
.
.
50% of SPAN = 4 + 8 = 12 mA
.
.
.
100% of SPAN = 4 + 16 = 20 mA
Hope this will be helpful to you.
Best Regards,
Jigar Anadkat
anadkat.jigar@gmail.com
| Is This Answer Correct ? | 2 Yes | 0 No |
TCD Principle
Dear all... I have 1 0-400 duplex type RTD, I connected the A side to the temperature indicator and B side to the PLC panel, but when I have observed then found that The PLC side temp has the variation. and it was distub to other RTD temp also. so what can I do.pls help me
IF PLC POWER FAILURE THEN WHAT HAPPEN?
WE ARE HAVING YOKOGAWA CENTUM CS 3000 DCS, 2 FCS AND 4 HIS " When the operation Download to HIS message appears: Equalize start. HIS0163 WARNING: Could not connect to equalize destination. (7001) Retrying. Number of retries = 0/1 ERROR: LdXopsLoadMain: connect error 10060 ERROR: LdXopsLoadMain: connect error 10060 ERROR: Processing terminated due to connection error. (7002) Equalization end with errors. HIS0163 ---- ERROR = 3 WARNING = 1 ---- Tell me, please, why and how to solve the problem."
6 Answers Khas Pvt Ltd, Yokogawa,
what is the PC interface and software for connection to ABB logic module “ LM011-CE18RAC “ ( for Programming ) ??
7. What are tri-state devices and why they are essential in a bus oriented system
A DP Endress and Hauser flow transmitter is always tripping pump at low flow. set point is 74 cubic meter/hr. Thorough impulse line flushing and zero calibration has been done, yet problem persists. What do you think is the problem and how do you rectify this fault?
where is a level displacer is used?
Which type of diaphragm use in costic line, dm water line, natural gas line, oil line?
Can we use mov instead of esdv Explain the reason
what are the programming languages used in dcs
How to check loadcell working or notworking
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)