If any control valve create hunting problem, what is the
possible reason and solution?
Answers were Sorted based on User's Feedback
Answer / imran
check as
1-put the controll valv in manual and check incoming signal
if stable then problem in controll valve
2- check positioner condition its feedback link ,incase of
smart poistener check feedback potentiometer.spring and
configration.
3-check diaphragam
4-gland packing
| Is This Answer Correct ? | 23 Yes | 0 No |
Answer / bhavesh
check the gland packing,check the positioner o/p is
unstable,check the small leakage on actuator.
| Is This Answer Correct ? | 8 Yes | 0 No |
Answer / muhammad arsalan afzal
1=First of all check the feedback link of positioner mostly
such type of problem occur due to feedback link looseness.
2=Gain of the controller is too high you have to adjust it.
3=Gland packing is too tight slightly lose the gland pusher's
screws.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / s.k.bakshi
1. First check the positioner air supply and the positioner.
2. If problem persists tune the PID.
| Is This Answer Correct ? | 8 Yes | 7 No |
Answer / suman chakraborty
check I/P signal means I/P and O/P whether the AFR o/p of I/P is stable or not.and check the AI Chanel of I/P.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / dhaval joshi
First check actuator position..removed power from the
actuator...and accordingly connect first power supply
cable,after connect command and feedback cable.
| Is This Answer Correct ? | 1 Yes | 6 No |
what is mean of 3 by 2 automation ?
why magnetic flow meter is not used in thermel power plant operation
Could anybody pls give ans of boiler 3 element control system?
What is the full form of PMMC ?
What is the difference between Analytical instruments and other instruments?
Is there’s power on the bus (if so, state whether on the signal bus, or on a separate in the following: a) HART b) Profibus DP c) Profibus PA d) DeviceNet e) Foundation Fieldbus
WHAT IS A SYMPTOM OF FAULT WITH THE SPAN OF AN INSTRUMENT? 1)ZERO-POINT AND 100% ARE CORRECT BUT NOT A MID-RANGE. 2)ZERO-POINT IS CORRECT ,BUT 1005 INPUT IS NOT GIVING 100% OUTPUT. 3)LINEARITY PRBS. 4)1005 O/p IS CORRECT BUT ZEO POINT IS WRONG.
What is CNC
how to calibrate absolute pressure transmitter
If we increase PI controller what will be action.
my data card only does run in my mobile so how can change it that it run other mobile & computer and i can stor data in my data card
what is air to open and air to close control valve and difference btwn this...and how to measure milli amp by this...and what is the role of positioner and i/p converter in this..plz help me
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)