why VCB are not used in 132KV system(above 33KV system)
Answers were Sorted based on User's Feedback
Answer / nihar ranjan mandal
Amount of vacuum required to quench the arc at 132 KV level
will be very high. It is difficult to maintain that amount
of vacuum in practical purpose. Now a days we use GIS( gas
insulated substation for 132KV level. Where arc is quenched
in hydrogen chamber.
| Is This Answer Correct ? | 16 Yes | 1 No |
Answer / karunakar
Ionisation at higher voltages causes arcing between breaker
contacts hence deteoriation of contactors. This raises
another methods for arc quenching.. so for medium voltages
currents upto 3000A VCB's have longer life and better
operability.
| Is This Answer Correct ? | 7 Yes | 2 No |
Degree of Vacuum required for quenching of ARC at 132 kV
level system fault is very high and its very difficult to
maintain that much degree of Vacuum so don't use VCB in 132
kV level. we generally used SF6 for this purpose.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / jobmon jacob
Factors contributing to interuptor selection are 1)voltage
2)metallurgy 3)vacuum 4)size 5)sc rating6)current chopping etc.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / raghu
In 132kv and above switch gear required very high vacuum to quenching arc during making/breaking the contacts, now a days we r using gas insulated and sf6 switch gears for proper operation.
| Is This Answer Correct ? | 0 Yes | 0 No |
what will be the minimum megger value for 132 Kv (earthed) potential transformer
What is the Diesel consumption between 82KVA DG Set and 180KVA DG Set for 1 hour.
there is an alternator 480 k.w, 400v,50hz, 4-wire running on load having leakage alternator body earthed current 38 A. is it within acceptable limit? if yes then give reference if no then how to bring within specified limit
what is transformer
What is expand formation of AYFY cable
what is the function of garing capacitir in SF6 circuit braker?
we have taken HV test of 2.5 k and Megger test on 11 kv HT cable.here it shows no fault but when we are charging the same cable with 11 kv supply why the VCB 11 kv gets tripped can anybody define the possible cause of fault ?
What is the difference bet ween EDO Type & MDO type ACBs, and what is the advantage EDO Type over than MDO type ACBs.
why test lamp didn't glow across 500v megger?
Two CTs 1600/1 and 35/1 are in series. while checking the ratio test of a CT(1600/1),same 1600A will also pass through the CT having ratio 35/1. Will it be harmfull to the ct(35/1),if yes , what will happen.CT secondary is shorted
In which connection the voltage will be more , in star or delta connected motor?
what is the significance of KV & MVA rating of the transformer and how they are related.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)