What is the difference between LT & HT Cable
Answers were Sorted based on User's Feedback
LT HT
1. Use : Up to 690V Above 690
2. Insulation : PVC XLPE
3. Core(Neutral) : Yes No
4. Insulation Grading : 1100 V Above
3.3kV, 11KV..etc
( Please note that now 690 V using in VFD application with
LV cable and 440 V for DOT motor starter)
Is This Answer Correct ? | 8 Yes | 1 No |
Answer / srikanth
it is depend upon the voltage rating when more than 700v
used is LT and for above it is HT..
Is This Answer Correct ? | 5 Yes | 2 No |
Answer / deepak singh kushwaha
lt cable are applicable for less than 700 volt with
neutral core but Ht cable is applicable 700 volt alongwith
without neutral core
Is This Answer Correct ? | 3 Yes | 4 No |
Answer / rakesh
HT CABLES ARE HIGH TENSION CABLES AND LT CABLES ARE LOW
TENSION CABLES.
Is This Answer Correct ? | 2 Yes | 6 No |
What is the temperature and cooling aspects of dc motor
If you don’t have coal, salt and copper, then how would you earth your connection temporarily at a camp site.?
What are the advantages & disadvantages of a group electrive drive?
what is self commutation how a thyristor discharges through a capacitor and inductor
in what type of applications v can use q meter?
What are the rating wise protections required for Generators from 600KVA to 2000KVA
What is the loss of power of transformer 220kv/33kv,63/80mva of % imp12.05 at 80%load
what is the difference b/w low voltage motors & medium voltage motors
what is fault level in 66kV system?
what is the function of avr when synchronous generator act as synchronous motor
two transformer connected in parallel.tap change are different.if i want to on the buscoupler what happen?
how do u gauge the size of the cable ?for eg. consider a 300 sqmm L.T Cable.How do u determine the size of the cable seeing it pratically?
0 Answers Bhel, Jai Balaji, Rashmi Group,