Even motor protection, why motor burn out ?
Answer / atul naik
Its not 100% true. Actually Motor has been protected many
a times before it actually burns. But either we have
ignored the actual reason of tripping by resetting OL
Relay or by removing the Over Load on Motor.
Still Motor Burns. So it is observed that following reasons
are there. 1 Dips in Supply Voltage, 2 Frequent Over Loads
reduces the performance/ sensitivity of OL Relay 3 Short
Ckt Protection is Not there (ANSI 50 & 50N )4 Short Ckt
Protection is Not Fast or delayed ( to avoid Nusence
tripping in Starting )5 Impairing of an Insulation due to
entry of unwanted gases,liquids etc,Reducing the Insulation
Strength of the Motor.,6 Wornout bearings, it will not only
oppose the motion and create resistance but also it
increases the heat / temp. 7 In case of CT Operated
Relays , CTs may reduce senstivity. Now, the cumulative
effect is that Fault Clearing Time is More than the Temp
rise time due to Fault , due to which Motor insulation
fails and motor winding no longer remain healthy ie Motor
burns.
| Is This Answer Correct ? | 19 Yes | 1 No |
During the main stator winding insulation testing (phase to ground)of 11kv alternator (Lerysomer) i found 0 and resistance with multimeter and found 20 killo ohm while the power cables are connected both end (Generator & VCB). In VCB PT (Potential transformer) are connected. Please any body explain that method of insulation is correct or not? also describe of PT connections
why we get 2 differnet values for power factor in 2 watt meter method in 3 phase
fuel-air ratio in a petrol engine fitted with suction carburettor,operating with dirty air filter as compared to clean filter will be
220/33kv voltage level having 60MVA rating , which transformer is preferred two winding or auto transformer. why, kindly provide your strong technical valuable views.
what its mean 'inverter based technology' ? if we talk about refrigerators, splits ACs etc how it helps to produce & keep more coolness and chilled atmosphere ?
why different series of vfds (like allenbradley)are used in industry ?
Which type of moter is used in trains, what is the ratting of supply used explain Working principal?
completed BE & done apprentice at tneb & having experience 6 years. want to get c license. will apprentiship & BE be helpful for getting c license. will i get any preference by showing this?
how to check avr of dg set of 125kva
how to decrese the PH value of liquid resistance?
What is the maximum load of 240mmsequre single core cable can carry?
What is Surge arrest? How it work?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)