How to calculate unit consumption on the basis of load.
kWH=kwXhrs.is it correct? kw is motor load.What is unit
consumption at 100% load, 50% load & on no load.
Answers were Sorted based on User's Feedback
Answer / satish m
For three phase motor we needs to consider the PF also.
P = Sq.Rt 3 X V x I x pf
Is This Answer Correct ? | 62 Yes | 8 No |
Answer / shannu
Unit consumption is KW x Hrs.
But while you need to calculate the KWH consumed by a motor,
multiplying KW of motor (nameplate KW) and hour will not
give you the energy consumed. This is because the name plate
KW in a motor is not the electrical power, but the
mechanical power output provided by the motor (Electrical
Power = Frictional losses + Eddy current losses + Copper
losses + air gap losses + Mechanical power). In order to
calculate the energy consumed by the motor you can use the
formula
single phase AC = Voltage x Rated current x Power factor x
Hrs run. (100% load)
3 Phase AC = 1.732 x Voltage x Rated Current x Power factor
x Hrs run. (100% load)
Normally the power factor of motor is considered between 0.8
to 0.85 at full load operation.
At no-load, motor will take approx 40% of its rated full
load current (again this depends on the design of motor, but
normally assumed to be near 40%). So at 50% load, the motor
will take a current around 70 to 75% of its full load rated
current. so we can approximate as
energy consumed at 50% load (motor - 3 phaase) = 1.732 x
Voltage x 75% rated full load current x power factor x Hrs run .
at no load = 1.732 x Voltage x 40% of rated current x power
factor x Hrs run.
Is This Answer Correct ? | 32 Yes | 7 No |
Answer / shivpal prajapati
kwh=kw*hrs is not correct.
kw=1.732*v.i.0.85,if motor rated current 64amp,
Then calculated value kw=1.732*415*64*0.85
Is This Answer Correct ? | 26 Yes | 9 No |
Answer / sakil belim
i have 70 hp 3 phase load. I run 70 hp in 1 hour in perday
what is kwh
Is This Answer Correct ? | 22 Yes | 8 No |
Answer / tushar amarghade
for 100% load
unit(kwh)- kw*hours/1000
where,
KW for single phase- V*I*PF
KW for THREE phase- 1.732*V*I*PF
Is This Answer Correct ? | 4 Yes | 1 No |
can we use 220 volt 15 w a.c. lamp on 220 volt d.c.
What is current chopping in CB?
In our factory so many iron pillors are exists for supporting the shed/Hangar. If do more no of earthings at one piller instead of doing more earth pits in many locations and running earth strip around the hanger, I can save the money. Please suggest this method is acceptable as per Is specifications though the Earth resitance of the farthest piller is with in the limits as per IS specifications.
What is UPS?
HOW TO WORK A VFD?SAY SIMPLE METHOD
Why PT burnts?
Enlist four components of electrive drives.
what is transformer
How many earthings are provided for a 250KVA distribution transformer?
IF ANY MATERIAL AVAILABLE IN MARKET FOR MOTOR PROTECTION INSTEAD OF OLR & CONTACTOR ?
which calss ct's,pt', use protection,meatering and others
What is balance beam relay ?