Answer / shantanu dash
The cable size of a motor mainly depends on the following
factors.
(i) Rated Current of Motor
(ii) Starting current and starting time of the Motor on
load.
(iii) Type of starters used for starting the Motor
| Is This Answer Correct ? | 75 Yes | 1 No |
Answer / govind
Thae cable size of the motor is decided from the rated load
(in Amps)of motor.
| Is This Answer Correct ? | 78 Yes | 9 No |
Answer / bhupatsinh
its depends on motor max. current, votage, and lenght of
cable.and volatage drop.
| Is This Answer Correct ? | 29 Yes | 1 No |
Answer / arvind
The cable size of motor depend on rated current of motor,
but as the motor draw more current at starting which will
be around 2-3times the rated current, so cable size will
going to be increased i.e, wherever we will calculate we
take 20% extra for selection of your cable
| Is This Answer Correct ? | 25 Yes | 6 No |
Answer / sanjeev pal
motor cable is decided according to motor rated current
given in specification plate. WHEN MOTOR is initially
running condition then motor draw current 1.5 times more its
rated current. so this factor decided cable size of motor
example 10 HP MOTOR rated current is 14.7 or 15 ampere
when initial running condition draw 1.5 times more
14.7 * 1.5 = 22.05 ampere then current caring capacity
of cable is 22 Ampere must be necessary.
correct answer hai
| Is This Answer Correct ? | 24 Yes | 11 No |
Answer / imran khan
Cable size of motor is decided on the following factors:
1. Full load current of motor(Since P=VICoso/Sqrt3VICoso)
2. Length of Cable.
3. Method of cable laying.(Air(Tray)/Underground(duct)).
4. Voltage drop of cable.
Calculation will be as:
1. If cable is laid on Tray/underground take its
corrosponding derating factors.
2. Multiply all derating factors & this derating factor is
multiplied by current carrying capacity of the cable which
you are going to sellect(from catalogue).
3. Above current should not be less than full load current
of motor.
4. Then check voltage drop (Vd=(IxLxmV/A/m)/(Rx1000))
where Vd=Voltage drop, I=Current(full load),L=length of
Cable(site requirement),mV/A/m=millivolt/Ampere/meter(from
catalogue),R=No. of Runs of cable.
5. Above voltage drop should not be more than 4%/2.5%(As
per requirement).
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / mithilesh
in Most of above answer every one stating about staring
current, current rating of motor but only one guy stated
about voltage drop of cable.
i think guy who stated about voltage drop,current rating,
power rating of motor( because starting current varies
with Hp rating of motor lower the hp higher the staring
current) his answer is more regionable than others.
from my experince i would say only full load current rating
of motor & voltage drop of motor will be enough to
calculate the cable size because staring current is only
for less time. and all cable has been designed for 2-3
times of rated current for 1 min. this answer will be
perfect for higher rated motor( more than 50hp)
less than 50 hp motor we have take consideration of
sttarting current( because starting current 3-4 times of
full load current).
is
| Is This Answer Correct ? | 7 Yes | 2 No |
Answer / md gufran yaqub
cable size for motor is decided based on
-rated load
-starting method and current withdrawn generally conductor
size is selected 2-3 times that of rated load
-length of cable and duty type decides the cable insulation
-obviously the cable rating should not be less than
protecting device
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / praful nandankar
To limit the starting current there are various protection
devices. Manufacturers always design the motor cable taken
into consideration the after effects of starting current.It
depends on the motor rated current and the voltage drop
which is already mentioned in some answers.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / dilanka
motor drowse starting current which will be around 2-3 times
the rated current. so cable size going to be increase.How
ever it is suitable to select 125% or 130% current rate for
cable because the cable can withstand without any damage for
few second. you must check the cable manufacturing data to
find this specific time and it should be more than the
starting time period of the motor.
| Is This Answer Correct ? | 0 Yes | 0 No |
which transmission is cheaper ac or dc?
limitation of conductor height on ground when we consider EMC
One 200 V, 100 W bulb is connected in series with primary of a 200 V, 10 kVA transformer. If its secondary is kept open circuited, then the bulb would have (1) Full brightness (2) Poor brightness (3) A little less than full brightness (4) More than full brightness...explain
What is the intent of short circuit studies?
Why high Voltages come in multiple of 11, like 11 KV, 33KV, 66 KV, 132 KV etc.
what is the CT & PT. where is it uses.what is the using that plese kindly answer me...?
What is 100% protection of generator? Why 95% protection is used not 100%?
sir, what is the importance of Fault MVA. how to calculate fault mva of 33kv substation connected by 6.5 km line(single circuit with equal spacing) with 110/11kv transformer in 110kv susbstation.the fault mva on 11 kv bus in 110kv susbstation is 208mva.
how we can use resistance heating for any domestic purpose???
Why are calling lagging power factor is a inductive load?
what is the differation bewreen kwh & fundamental kwh in electronic trivector meters
Transformers with dc supply
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)