What is 100% protection of generator? Why 95% protection is used not 100%?..

Answer / aswin joseph

95% stator earth fault protection uses an overvoltage relay at the neutral transformer of a generator. Because there is always a minimum voltage at the neutral because of harmonics and zero sequence, a little margin is necessary and only 95% of the generator windings can be covered with this method.
100% stator earth fault protection uses current injection at low frequency or minimum third harmonic voltage to detect earth faults. It does not have the limitation at the earth side of the winding, so using this method and the one described for the 95% you can cover 100% of the stator.
Both detect earth faults at generator stator windings when generators neutrals are connected to earth using neutral transformers or reactance, which make neutral currents too small to use overcurrent relays.
Injection method protects 100% stator windings without the need of a 95% relay. It works on its own.
The principle is the following: a signal generator injects voltage pulses in the windings of the machine at a frequency different from the rate frequency of the system or any harmonic (typically 10 Hz to 25 Hz, 87 Hz...). These pulses are transmitted to ground through the winding insulation and back to the signal generator through the earthing resistor.
Together with the signal generator, the relay also measures the current in the signal injected. In normal conditions, total impedance is high and low currents are measured. If there is a phase to earth fault in any phase, impedance to ground decreases and current increases rapidly, indicating the fault.
This method works even with the machine out of service if the relay is connected (careful with this during maintenance).
This system is normally implemented at the generator neutral transformer, but if it is not available (for example, because a resistance or reactance is used instead of a transformer, or the generator is delta connected), voltage transformers can be connected at the generator terminals with the secondary connected in broken delta, since this allows the injection of the same signal to all windings.

Is This Answer Correct ?    32 Yes 7 No

What is 100% protection of generator? Why 95% protection is used not 100%?..

Answer / shailesh tankni

generators are basically synchronizing machine if a fault
occurs, they fall out of synchronization. but if the fault
is temporary or for a very small duration micro seconds or
seconds then the alternator/ generator may again achieve
synchronization without permanent interruption of supply.
this is the reason why the 95% protection is provided
instead of 100% protection.

otherwise for even for the small fault we would experience a
cut off eg: a small fault like contact of two phase
conductors due to sudden wind. which is a temporary fault.

Is This Answer Correct ?    42 Yes 36 No

What is 100% protection of generator? Why 95% protection is used not 100%?..

Answer / dayanidhikinkar

since few turns of wdg have very small voltage therefore
fault current flowing through secondary of CT is less than
preset value for relay operation.Hence relay will not
operate for that much portion of winding.

Is This Answer Correct ?    11 Yes 8 No

What is 100% protection of generator? Why 95% protection is used not 100%?..

Answer / m bhargava narayana

for 0-95% stator earth fault over voltage relay is used,where as 95-100% earth fault(because small amount of third harmonic zero phase seq currents flow through neutral induces small voltage at neutral) under voltage relay is used.

Is This Answer Correct ?    1 Yes 1 No

What is 100% protection of generator? Why 95% protection is used not 100%?..

Answer / dr. s.r.krishnamurthy

If a fault occurs at say 98%th portion of generator phase
winding reconed from the phase terminal, the voltage
induced in that balance 2% winding is not sufficient to
drinve a fault current through the differential relay.
Hence intentionally 100% protection relay is not used.

Is This Answer Correct ?    2 Yes 8 No

What is 100% protection of generator? Why 95% protection is used not 100%?..

Answer / sandip upare

Generator having lot of protections rotar-stator wdg. earth
fault,over voltage,over current etc.
For that each relay having setting from 0-100 per. with
time period in seconds
According to type of fault we have to set the setting

example :- for earth fault protection we have set upto 50-
70per. because if we set to 100% every and each small
leakage relay trip

so my thinking is only that the setting of each protection
is depend up application of DG only on what load

Is This Answer Correct ?    18 Yes 25 No

What is 100% protection of generator? Why 95% protection is used not 100%?..

Answer / vijaybharadwaj202

to provide the 100% protection for alternator ,it interrupts
the operation of generation even low level faults, so we can
provide protection for alternator 95% instead of 100%

Is This Answer Correct ?    5 Yes 13 No

What is 100% protection of generator? Why 95% protection is used not 100%?..

Answer / rohit singh

Because in the case of Generator if we choose the 100%
protection then the protection system cost more than the
generator cost. thats why we will choose 95% of protection.

In India generally 92-93% protection is used whereas inother
country it is 95-96%.

Is This Answer Correct ?    5 Yes 16 No

What is 100% protection of generator? Why 95% protection is used not 100%?..

Answer / dalveer

BECAUSE IF WE USE 100% PROTECTION FOR THE GENERATORS THEN
IT CAN'T BE WORK PROPERLY. IF ANYONE HAVE ANY DOUBTS THEN
CALL ME...... 09729722179

Is This Answer Correct ?    3 Yes 70 No

Post New Answer

More Electrical Engineering Interview Questions

while doing the excitation current test on power transformer what is the value of voltage to be applied? Nomonal rated voltage or 10% of rated voltage? Is it necessary to apply on high voltage side?

1 Answers   ACC,


What is Procedure the procedure to select CT's & PT's in 66kV and above substation?

2 Answers   BEL,


why we did not mention ryb like byr in 3 phase

2 Answers   Ford,


What is the difference between AVR and Servo Stabliser

3 Answers   Wipro,


What is the maximum operating temperature for a thermoplastic insulated cable?

0 Answers  






sir i am apearing for nic exam.i dont know exam pattern.can you please send me some model papers

0 Answers  


If there is volagte between earth and neutral, what should be the reason ? and solution * What should be allowable limit in case, if the voltage between earth and neutral exist ? / OR what is limit for safe voltage between earth and neutral?

3 Answers  


Ceiling fan motor wiring Hi, I have 2 ceiling fans broken. The receiver/control units burned out due to lightening. One Harbor Breeze and one Hunter's I took them apart (remove receiver units). Now on both of the motor I see 4 wires coming out from each motor I really want to know the function of each wire. Are there anyway I can test to see which is which? After searching forums I know these 4 wires are from 2 sets of coils inside the motor, one is Start winding and the other is Runing winding I could not find the receiver/control unit any where, so I am planing to buy Capacitors and universal remote controls to make the fans run again. Anyone has any idea how to do the wiring, please help Thnks

1 Answers  


whether fibre optic cable in high voltage earth conductor is used for protection circuits

0 Answers  


What should be the magnetic balance test values for a 3 phase delta/star connected single primary dual secondary winding transformer (90 MVA / 2 X 45 MVA TRANSFORMER)

0 Answers  


how to calculate short circuit calculation of the transformer by usuing the percentage impedence? formula needed.

2 Answers   L&T,


why the capacity of power plant is given in MW though the generators are rated in MVA?

3 Answers   TATA,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5084)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)