What is 100%
protection of
generator? Why
95% protection
is used not 100%?
Answers were Sorted based on User's Feedback
95% stator earth fault protection uses an overvoltage relay at the neutral transformer of a generator. Because there is always a minimum voltage at the neutral because of harmonics and zero sequence, a little margin is necessary and only 95% of the generator windings can be covered with this method.
100% stator earth fault protection uses current injection at low frequency or minimum third harmonic voltage to detect earth faults. It does not have the limitation at the earth side of the winding, so using this method and the one described for the 95% you can cover 100% of the stator.
Both detect earth faults at generator stator windings when generators neutrals are connected to earth using neutral transformers or reactance, which make neutral currents too small to use overcurrent relays.
Injection method protects 100% stator windings without the need of a 95% relay. It works on its own.
The principle is the following: a signal generator injects voltage pulses in the windings of the machine at a frequency different from the rate frequency of the system or any harmonic (typically 10 Hz to 25 Hz, 87 Hz...). These pulses are transmitted to ground through the winding insulation and back to the signal generator through the earthing resistor.
Together with the signal generator, the relay also measures the current in the signal injected. In normal conditions, total impedance is high and low currents are measured. If there is a phase to earth fault in any phase, impedance to ground decreases and current increases rapidly, indicating the fault.
This method works even with the machine out of service if the relay is connected (careful with this during maintenance).
This system is normally implemented at the generator neutral transformer, but if it is not available (for example, because a resistance or reactance is used instead of a transformer, or the generator is delta connected), voltage transformers can be connected at the generator terminals with the secondary connected in broken delta, since this allows the injection of the same signal to all windings.
| Is This Answer Correct ? | 32 Yes | 7 No |
Answer / shailesh tankni
generators are basically synchronizing machine if a fault
occurs, they fall out of synchronization. but if the fault
is temporary or for a very small duration micro seconds or
seconds then the alternator/ generator may again achieve
synchronization without permanent interruption of supply.
this is the reason why the 95% protection is provided
instead of 100% protection.
otherwise for even for the small fault we would experience a
cut off eg: a small fault like contact of two phase
conductors due to sudden wind. which is a temporary fault.
| Is This Answer Correct ? | 42 Yes | 36 No |
Answer / dayanidhikinkar
since few turns of wdg have very small voltage therefore
fault current flowing through secondary of CT is less than
preset value for relay operation.Hence relay will not
operate for that much portion of winding.
| Is This Answer Correct ? | 11 Yes | 8 No |
Answer / m bhargava narayana
for 0-95% stator earth fault over voltage relay is used,where as 95-100% earth fault(because small amount of third harmonic zero phase seq currents flow through neutral induces small voltage at neutral) under voltage relay is used.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / dr. s.r.krishnamurthy
If a fault occurs at say 98%th portion of generator phase
winding reconed from the phase terminal, the voltage
induced in that balance 2% winding is not sufficient to
drinve a fault current through the differential relay.
Hence intentionally 100% protection relay is not used.
| Is This Answer Correct ? | 2 Yes | 8 No |
Generator having lot of protections rotar-stator wdg. earth
fault,over voltage,over current etc.
For that each relay having setting from 0-100 per. with
time period in seconds
According to type of fault we have to set the setting
example :- for earth fault protection we have set upto 50-
70per. because if we set to 100% every and each small
leakage relay trip
so my thinking is only that the setting of each protection
is depend up application of DG only on what load
| Is This Answer Correct ? | 18 Yes | 25 No |
Answer / vijaybharadwaj202
to provide the 100% protection for alternator ,it interrupts
the operation of generation even low level faults, so we can
provide protection for alternator 95% instead of 100%
| Is This Answer Correct ? | 5 Yes | 13 No |
Answer / rohit singh
Because in the case of Generator if we choose the 100%
protection then the protection system cost more than the
generator cost. thats why we will choose 95% of protection.
In India generally 92-93% protection is used whereas inother
country it is 95-96%.
| Is This Answer Correct ? | 5 Yes | 16 No |
Answer / dalveer
BECAUSE IF WE USE 100% PROTECTION FOR THE GENERATORS THEN
IT CAN'T BE WORK PROPERLY. IF ANYONE HAVE ANY DOUBTS THEN
CALL ME...... 09729722179
| Is This Answer Correct ? | 3 Yes | 70 No |
why restricted earth fault protection can not operate for phase faults??as there will be a current in secondary of ct,when a phase fault occurs!
what instruments used for measuring of inductance and capacitance.
why ups rating in kva? and why ups are in parellel?.why isolation transformer is used in ups?
why delta delta connection generally not use in transformer
what is the diffrence between resistive load and capoasitive load.?
In a company the lines carrying 33KV but the load is below 10000Volts so we know that <11KV we can put 11KV lines but the lines are 33KV,..so how we can step down the voltage to 11KV with out erecting a substation
What must be the minimum distance maintained between 2 Generators as per International standards?
I want definition for ABT Meter (Availability Based tariff) ?
0 Answers Radha Regent Hotels,
Difference between megger test equipment and contact resistance meter test instruments?
What is the feedback in the control system?
what is power and what is watts detailed description and formulas
what is efficient load of transformer in percentage
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)