What's the part of OTCC in transformer?
Answers were Sorted based on User's Feedback
Answer / d.sanadi
OTCC??? it should be either OCTC(OFF CIRCUIT TAP CHANGER)
OR OLTC (ON LOAD TAP CHANGER). Tap changers are basically
used to adjust the secondary voltage to a range of +/-5%
Is This Answer Correct ? | 21 Yes | 2 No |
Answer / b.krishnaswamy
OCTC- Off circuit tap changer is meant for changing the
secondary voltage of power transformer within the rated
plus minus range with respect to the rated nominal
secondary voltage by shifting the tap positions.. As the
name implies the taps are changed only when the transformer
is taken off the circuit.
Is This Answer Correct ? | 16 Yes | 2 No |
Answer / sudhakar ghait
OLTC - ON Load Tap Changer. When primary voltage low/high
in that condiction we will maintain our secondary voltage
by using our transformer's OLTC
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / b.krishnaswamy
It should be OCTC-off-circuit tap changer or OLTC- On-load tap changer. OCTC is for changing the taps provided in HV side of the transformer when the transformer is out of cicuit , as the name implies, for changing the voltage ratio. In OLTC the taps can be changed when the transfomer is on load. The number of taps provided depends on the design requirements for change of secondary voltage on the + side and minus side relative to the rated voltage ratio.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / jalees divker
Question May be regarding RTCC
if it that mean remote Tap changing cubicle, this cubicle normally installed in control room/or any suitable place, to change the Tab of transformer ,whenever desired as per Grid voltage, It could be Manual/Auto operated.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / venkatesan.j
It is a part of the HV winding ,as the current is low. It
is used to step up or down the voltage according to the
requirement.
Is This Answer Correct ? | 1 Yes | 4 No |
difference between ac and dc motor
what happen when transformer connect on dc supply.
What is the typical enclosure type used for Indoor switchgear / Outdoor switchgear Units? - In Onshore / offshore Units?
oil cooled transformer
how can we check a fully charged battery?
6 Answers BEML, Singareni Collieries,
How to calulate cable size for 200KVA,160KVA& 40KVA load?
What will be the fault current of any system when its generation is 10% of BASE generation( FUll Load )?Will is 10% or the same as full base calculation?
wat is the difference between rotor 1st stage fault and 2nd stage fault?
how synchronous condenser is used in place of synchronous generator with out negotiating IEEE standards? Can i use 3 generators as synchronous generators and 2 generators as a synchronous condensers in an IEEE 14 bus system with out disturbing the standards?
why power is generatd at 50 hz only..? can we do this on another freq...?
Is it possible to protect 3phase overload and earth fault of the 3phase system using two CT's.
Wat will happen if R-phase of an alternator is connected to B- Phase of AMF panel fed from alternator