Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


how to choose the cable rating for load (KW)? EXAMPLE.50KW load

Answers were Sorted based on User's Feedback



how to choose the cable rating for load (KW)? EXAMPLE.50KW load..

Answer / vinod sharma

In a three phase system p=1.732x3xVxIxCOS@
When load is given 50KW
Then I=50000/1.732x3x415x.8
=86A near about
taking some future expectancy you can take a cable of
having 100A capacity.SO by this u can take a cable of 70mm
square in aluminium and 50 mm square in copper

Is This Answer Correct ?    230 Yes 138 No

how to choose the cable rating for load (KW)? EXAMPLE.50KW load..

Answer / engineer

Right cable size Sellection depends on 3 factors:
1- Load Current.current(I) = 50kW /(1.732*415*0.85
(p.f)) =139A

2- Distance(From feeder to your load)
3- Allawable Voltage droop in your system (Should be less
than 5% )

As experience you can use 10sqrmm for 40A,for 120meter.

Is This Answer Correct ?    117 Yes 52 No

how to choose the cable rating for load (KW)? EXAMPLE.50KW load..

Answer / mohammad farman khan

Fisrt calcultate Load in Ampere as basic formula below

I (Amp ) = P ( KW) / 1.732*Voltage (400 or 415 or 380 )*
p.f

Voltage depend on frequency rating (50 Hz or 60 Hz)
then check where you have to laid in AIR or Ground
you have to consider so many factor.
suppose you laid in Ground then factor to be consider as
below
(1) Soil Thermal Rseistivity
(2) Group factor
(3)Rating factor of ground temprature
(4)Rating Factor depth of laying

then calculte Voltage drop on behalf of amper rating by
load.
once you calculate then check length

V.D = mv x I X L/1000 OR mv =V.D X 1000/IXL

VD= Maximum acceptable volt drop (in volt)
mv =appropriate volt drop (in mv /amp /metre
I = Current per phase (in ampere)
L= Length ( in meter)

Is This Answer Correct ?    50 Yes 15 No

how to choose the cable rating for load (KW)? EXAMPLE.50KW load..

Answer / sunil patil

Given- KW-50
Now from formula I= KW X1000/(V X I X 1.732 X .8)
=86.95 A
Now by refering fenolex cable rating table
For 25mm2 =80A Which is less than our o/p current so we
can select 35mm2 having current capacity is 102A

Is This Answer Correct ?    36 Yes 12 No

how to choose the cable rating for load (KW)? EXAMPLE.50KW load..

Answer / m.saad

Calclate the load Current
I = p/((root3)*V*P.F )
where I line current, v line voltage
then go to cable tabe
and check the Drateing factors.such as
if this cable underground,free,soil,depth of laying,
ambient temperture, armoed or unarmoed etc.

then calcute the voltage drop
if more than 4%
you should to select the next bigger cross section at table.

by experince for copper PVC cables
1mm take 2.5 AMP

Is This Answer Correct ?    32 Yes 13 No

how to choose the cable rating for load (KW)? EXAMPLE.50KW load..

Answer / shabeeb

50kw load will take 87 amps (approx.). There is table of
different types of cables available in the manufactures
site. More over there is so many factors are there to
select a cable. Such as the type of material (copper /
aluminium), single core or multicore, how and where the
cable is being laid, the length of cable(for voltage drop
calculation), type of load and its starting current (for
motors), future load etc. Normally if the load is 50KW,
70sq.mm Aluminium cable or 50sq.mm copper cable can be used.

Is This Answer Correct ?    29 Yes 16 No

how to choose the cable rating for load (KW)? EXAMPLE.50KW load..

Answer / ajith

380V/50HZ,50KW=4core50mm

Is This Answer Correct ?    12 Yes 9 No

how to choose the cable rating for load (KW)? EXAMPLE.50KW load..

Answer / mathhar

LOAD : 50kW , 415V , 0.8p.f
1- I = 28.75A
2- 28.75 * 1.2 = 34.5A
3- temp. factor * group factor = 0.75 "ex."
4- 34.5/.75 = 46A
5- choose 16mmsq
6- cal. Vd = (I * L(m) * delta(v)/ (V * 1000))*100%
its should less than 5%
7- short circuit temp. rise

Is This Answer Correct ?    19 Yes 17 No

how to choose the cable rating for load (KW)? EXAMPLE.50KW load..

Answer / imtiaz ahmed

i m an engineer and i want to formula to calculate the size of cable in the form of load killowatt
kindly send me this formula wi appropriate example even then i understand easly.
this will be your greatness.


thanks and regards
imtiaz ahmed
from kashmir
cell no +92 345 9748199

Is This Answer Correct ?    1 Yes 1 No

how to choose the cable rating for load (KW)? EXAMPLE.50KW load..

Answer / electrical engineer kaleem 055

As my 5 years of experiance. I am still working in construction field as Electrical Engineer. Let me tell you 1 easy and good method to find the cable size for load , Earth cable size for load and to find the exact circuit breaker size which is require for load.
Always keep it in your mind that if load will 30kw or 20kw or 50kw etc always select the cable size 1 step down from the given load.Example for 30kw load cable size will be 25sqmm. and for 20kw it will be 16sqmm.etc
for earthing cable always load divided by 2. Example for 30kw load earth size will be 15 but in market 15 is not available so use 16sqmm yellow green cable and for 20kw load use 10sqmm cable etc.
Now for circuit breaker.
Always load multiple by 2 so that will be your mcb size.
Example if you are using 30kw load
30 x 2 = 60 so you will use 60 ampear mcb for 30kw load.And for 20kw use 40ampear breaker.

Is This Answer Correct ?    0 Yes 2 No

Post New Answer

More Electrical Engineering Interview Questions

what can i do line to line fault

4 Answers  


hi I have done 3 yrs diploma in electrical engg after 10+2. I have 16 years of work experience into design proposals sales and engg application development in LV/MV swithcgear and sub station automation field. I want to apply for immigration to new zealand but I am not sure whether I qualify or not since I dont have a degree. Can anyone advice? Thanks Riz

0 Answers  


Why NGR is required for 11Kv geneartor in power plant

2 Answers   AB Inc, ABB,


State how to produce a constant rotating field by application of alternating currents to stator armature of a three-phase squirrel-cage induction motor

0 Answers   Jindal,


what is sevice settings for mccb?How can be it setted?

0 Answers  


When placed close together, two positively charged materials will

1 Answers  


V.c.b and a.c.b difference

4 Answers  


hai...... tis is Hemanth. jst now completed electrical engineering... i wanna to apper for ap tranco exam... plzz send me the previous q's paper link......thanx in advance.

0 Answers  


Why we not use the impedance relay in protection of short transmission line ?

4 Answers  


hello freinds what is advantage and disadvantage of plc again dcs?

2 Answers  


Why DC excitation is used for alternators? Why cant it be AC?

35 Answers   ABB, Ace Info, Alstom, Shalivahana Power,


In AC if the direction of current keeps reversing every half cycle, how does it propogate through the transmission lines?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)