how to choose the cable rating for load (KW)? EXAMPLE.50KW load
Answers were Sorted based on User's Feedback
Answer / er.p.somasundaram
1 H.P = 1.25 Amps
IN CASE ALUMINIUM CONDUCTOR USE CONSTANT VALUE IS =0.75
IN CASE COPPER CONDUCTOR USE CONSTANT VALUE IS =1.25
SO CONDUCTOR SIZE= 1.25*1.25(CU)=1.25SQMM
| Is This Answer Correct ? | 26 Yes | 35 No |
Answer / er.p.somasundaram
10 H.P = 10.25 Amps
IN CASE ALUMINIUM CONDUCTOR USE CONSTANT VALUE IS =0.75
IN CASE COPPER CONDUCTOR USE CONSTANT VALUE IS =1.25
SO CONDUCTOR SIZE+cable sqmm *075 =10.25amps, now a days increase current so cable size is small size increases.
10.25*0.75=10 sq mm
| Is This Answer Correct ? | 15 Yes | 33 No |
Cable carring capasity is there.. we can get form cable
manufacturer...
for 50kW load,
current(I) = 50/(1.732*415*.8(p.f))
I = 28.75A
For 1.5Sqmm cable curent carring capasity = 20A in ground
2.5 = 27,
4 = 34,
6 = 43,
10 = 57,
16 = 73A like that.
now our load current is 28.75A
No.of cable with size =28.75/43A (6Sqmm)
= .6686/.7 (Diff factor)
=.955
there fore 1run 6 Sqmm aluminium cable we selected for 50
kW load.
| Is This Answer Correct ? | 31 Yes | 153 No |
Answer / suresh kumar
Copper Cable: Sqmm*1.5, Exam: If we have 50 Sqmm copper
cabe, The it will take load is 50*1.5=75Amp
Al Cable is multiplying factor of 1.
Exam: 50 Sqmm cable will take 50A load.
| Is This Answer Correct ? | 98 Yes | 233 No |
Why we connect the capacitor in Delta?if we conect in Star what will happen?
Is it possible to make 0.75KW motor earthing from MCC panel by using the 1.5 SQMM, 4 core cable, means 3 core for 3 Phases & 1 core for Earth terminal?
what's the thickness of 1.5sqmm wire
whatare the disadvantages occur,if the form factor of transmission will not be equal to 1.11
what is the difference between arc and spark
why use only sf6 circuit breker in 400 kv sub station
A 40 kva transformer has a core loss of 400W and a full load copper loss of 800W. What is The proportion of full load at maxmimum efficiency?
What will be the total current for 300kva UPS if it runs on 40 to 45 percent load. Is there any formula for to calculate the exact load.
Do closed loop systems require manual input?
what is the dis-advantage of 3 phase 3 wire energy meter?
What will happen if power transformer designed for 50 Hz is connected to 500 Hz of the same voltage , and vice versa ?
The simple way of finding the leakage quantity and % in compressed air distribution system
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)