Determine the manipulated variable, controlled variable,
and the measured variable given a description of various
typical industrial processes.
Answers were Sorted based on User's Feedback
Answer / ecxlsync
* Manipulated variable is the one being manipulated by the
final element(usually control valve) to correct the error.
* Controlled variable is the one being controlled or the
desired process value according to the SP.
* Measured Variable is the output of the measuring device.
example water temperature control:
there is a heat exchanger. the are 2 inlets of this exchanger
which is hot and cold water. the hot water must be cool down
when it leaves the exchanger at a certain temperature being
defined by the SP. a control valve installed at the cold
water inlet line to control the flow of cold water. the cold water flow at the control valve downstream is the MANIPULATED VARIABLE. the temp of hot water discharge from exchanger which has attained the setpoint value is the CONTROLLED VARIABLE.
| Is This Answer Correct ? | 35 Yes | 4 No |
Answer / shasha
a manipulated variable is the one you change to see what
happens to the "responding" variable
a "responding variable is the one that changes in response
to your changing the manipulated variable
The controlled variable(s) is (are) the one(s) that you hold
constant and don't allow to change
For example: Let's say you're doing an experiment to find
out if drinking lots of Kool-Aid makes you stronger. You
take two groups of people, and you feed them exactly the
same things, EXCEPT that Group A gets lots of Kool-Aid and
Group B gets lots of water.
Manipulated variable: Kool-Aid. One group drinks lots, the
other drinks none.
Responding variable: How strong the person is. One group
will demonstrate that they can (maybe) lift some amount of
weight. Can the other group lift that, too?
Controlled variable: All other aspects of the diet, e.g. how
much they're eating, what kinds of food they eat, how much
candy. These are all kept identical between the groups.
• 10 months ago
| Is This Answer Correct ? | 17 Yes | 5 No |
Answer / ahmed helmy
- Manipulated variable is the output of controller to final control element to correct the error sometimes called also output
- Set point is the desired value for the process
- Controlled variable is the process variable which is the output of the process and measured by the transmitter
- Measured variable is also the controlled variable
- process variable = controlled variable = measured variable
| Is This Answer Correct ? | 9 Yes | 3 No |
Answer / a
PROCESS VARIABLE - Sensor O/P value in the form of 4-20ma
corresponds to Actual value after conditioning.(say level)
Example: Radar Lvl TX
SET VALUE - Required Process value to make the system
stable.
Example: Actual Tank lvl 100%
Required Lvl (to be maintain) 70%
MANIPULATED VARIABLE - Output Signal(4-20ma) required to
maintain the process variable near to setpoint.
Example: Control valve action to fill the tank.
| Is This Answer Correct ? | 14 Yes | 9 No |
Answer / ram
The variables that are manipulated to have control over the process variable is called "manipulated variable"
Eg. Level is maintained by closing or opening the control valve ; here control valve position is "mv"
According to this example , both PV and CV ....is the level of the water in tank
| Is This Answer Correct ? | 4 Yes | 2 No |
let e---error,r--setpoint(reference),b--feedback(measured
variable), m---manipulated variable, c---controlled variable
Now
1)e=r-b
2)c=(Control action*e) + Bias
3)m= c(after final control action)
| Is This Answer Correct ? | 13 Yes | 13 No |
HI, can anybody give details about GAS TREATMENT PLANT CONSTRUCTION,as INSTRUMENTATION ENGINEER what are the responsibilites.what are the instruments mainly instrumentation engineer will deal with
Hi buddies! my name is sachin and i am working as a electrical and instrumentation engineer in a paper plant. right now i am facing a problem and if someone could help me it will be an immense pleasure to me. i am using AC 800M to synchronise DCS500 drives on paper machine and rewinder.communication is on PROFIBUS and we are using NPBA-01 module to link profibus to DC drives.But these days two of these drives are showing a error named FIELDBUS COMM.TIMED OUT and the drives get tripped.I have changed the NPBA module and PROFIBUS cable.So if anyone can do please help me out with this problem.I'll be highly grateful.
What is protocol ?
Why we used cage in control valve?
how control valve works?
what is the operation philosophy of proximity velocity sensor
Transmitter reading is zero but in DCS showing one Bar what is the reason ?
why we are using ungrounded RTD sensor and what is difference between grounded RTD and Ungrounded?
What is the role of Integral in pid control?
In instrumentation standard we use 4 to 20ma for transmission , why cant we use 3 to 19ma ?
how to calibrate the radar transmitter for measuring the exact tank level if tank is having agitator moving continiously because due to agitator tank surface level will vary every time.
this site is owned by an nonsense
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)