Determine the manipulated variable, controlled variable,
and the measured variable given a description of various
typical industrial processes.
Answers were Sorted based on User's Feedback
Answer / ecxlsync
* Manipulated variable is the one being manipulated by the
final element(usually control valve) to correct the error.
* Controlled variable is the one being controlled or the
desired process value according to the SP.
* Measured Variable is the output of the measuring device.
example water temperature control:
there is a heat exchanger. the are 2 inlets of this exchanger
which is hot and cold water. the hot water must be cool down
when it leaves the exchanger at a certain temperature being
defined by the SP. a control valve installed at the cold
water inlet line to control the flow of cold water. the cold water flow at the control valve downstream is the MANIPULATED VARIABLE. the temp of hot water discharge from exchanger which has attained the setpoint value is the CONTROLLED VARIABLE.
| Is This Answer Correct ? | 35 Yes | 4 No |
Answer / shasha
a manipulated variable is the one you change to see what
happens to the "responding" variable
a "responding variable is the one that changes in response
to your changing the manipulated variable
The controlled variable(s) is (are) the one(s) that you hold
constant and don't allow to change
For example: Let's say you're doing an experiment to find
out if drinking lots of Kool-Aid makes you stronger. You
take two groups of people, and you feed them exactly the
same things, EXCEPT that Group A gets lots of Kool-Aid and
Group B gets lots of water.
Manipulated variable: Kool-Aid. One group drinks lots, the
other drinks none.
Responding variable: How strong the person is. One group
will demonstrate that they can (maybe) lift some amount of
weight. Can the other group lift that, too?
Controlled variable: All other aspects of the diet, e.g. how
much they're eating, what kinds of food they eat, how much
candy. These are all kept identical between the groups.
• 10 months ago
| Is This Answer Correct ? | 17 Yes | 5 No |
Answer / ahmed helmy
- Manipulated variable is the output of controller to final control element to correct the error sometimes called also output
- Set point is the desired value for the process
- Controlled variable is the process variable which is the output of the process and measured by the transmitter
- Measured variable is also the controlled variable
- process variable = controlled variable = measured variable
| Is This Answer Correct ? | 9 Yes | 3 No |
Answer / a
PROCESS VARIABLE - Sensor O/P value in the form of 4-20ma
corresponds to Actual value after conditioning.(say level)
Example: Radar Lvl TX
SET VALUE - Required Process value to make the system
stable.
Example: Actual Tank lvl 100%
Required Lvl (to be maintain) 70%
MANIPULATED VARIABLE - Output Signal(4-20ma) required to
maintain the process variable near to setpoint.
Example: Control valve action to fill the tank.
| Is This Answer Correct ? | 14 Yes | 9 No |
Answer / ram
The variables that are manipulated to have control over the process variable is called "manipulated variable"
Eg. Level is maintained by closing or opening the control valve ; here control valve position is "mv"
According to this example , both PV and CV ....is the level of the water in tank
| Is This Answer Correct ? | 4 Yes | 2 No |
let e---error,r--setpoint(reference),b--feedback(measured
variable), m---manipulated variable, c---controlled variable
Now
1)e=r-b
2)c=(Control action*e) + Bias
3)m= c(after final control action)
| Is This Answer Correct ? | 13 Yes | 13 No |
where are following valves are applicable to install. can any valve be installed any line. globe valve butterfly valve boll valve gate valve
diff between neutral ,ground,phase , earthing and shielding?
My rtd working well at the same time r/i converter is not working properly.when power is given to rtd..it is giving 30mA and getting 2.4 mA if i remove the compensate leads No matter how many ohms.why it is happening like so?what is the solution?rtd range-0-200deg c& 4-20 mA o/p.please give me solutiin anyone......
plz... clarify my answer, how to calibrate vaccum (DP)leveltransmitter,it is hart. (digital).DETAILS:(coloumn)closedtank height 2650mm,and tx range is 0-1500mmH20.
Explain the difference between mmwc and mmwg?
How many mode are in ups?
types of valves
3 Answers Bindal Papers, Kuwait Oil Company,
How to do manual mapping in radar type level transmitter?
A differential transmitter is calibrated to measure the flow of lquied, explain what wil happen if the fluid is not pure but contains some bubble?
How the flow can be measured by using DP Transmitter?
1. What is the main differences between GE Mark IV and Mark V Turbine Control System? 2. what is the main differences between GE Mark V and Mark VI?
If any control valve create hunting problem, what is the possible reason and solution?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)