How we can do the linearity test for Bently Naveda
Vibration Probe?
Answer / ahmed sabry
first, we have 3 main types of Bently vibration probes:
1 - Proximity probe
2 - Accelerometer probe
3 - Key phasor probe
For proximity probe, we have 2 types:
1 - displacement probe for axial forces measurement.
2 - velocity probe for radial forces measurement.
Both tyes of probes are calibrated using a suitable calibration kit supplied by the vendor, the calibration kit simulate the shaft vibration and can be used to check/adjust the probe and the monitor.
I have a practical experience with 3300 system which give the output through "proxomiter" from terminals output & ground - for normal case it has to give "-10 vdc" and we have 200 mv for every 1 mil diplacement.
This is an example of used calibration kit:
http://www.ge-mcs.com/download/sensors-and-transducers/141580.pdf
==========
If we need to Check/calibrate the rest of the vibration loop (monitor check), We will need a function generator & multimeter.
For the monitor we will inject in the Monitor card by the function generator a combination voltage of -7 dc voltage with AC voltage with suitable freq.(follow the manual to specify the values of AC, DC and freq.).
For axial vibration monitor we will vary the DC amplitude and check the results on the monitor.
For radial vibration monitor we will vary the AC amplitude and check the results on the monitor.
Best of luck
Ahmed Sabry
Instrumentation & Control Engineer
Mob: +2 0122 1367310
| Is This Answer Correct ? | 18 Yes | 1 No |
I have applied the post Junior Engineer-(TM)in R.R.B CHANDIGARH recently . what type of question i have to practice and which book ?. can i get any model question paper?
Draw a P& ID showing – orifice flange, plate, dp transmitter, isolation & bypass valves and tubing.
Operational amplifiers
What is the solution if rotork motorised control valve showing pink Colour in dcs.
3 Answers Bhushan Power Steel,
why most of the DP transmitters using maximum range as 0-2500mmwc?why not 1000 2000 3000 4000mmwc
What is standard of DCS panel design?and what is step of DCS panel design?wiring and type of connector(screw or DB connector)
Please explain about FAT? What is the difference between FAT and SAT?
Which standard of hazardous area classification used in India?
we re giviang 24v supply to transmitter and we getting output from tx?now my question is wht we call this complete proces?
what is the difference between transmitter and converters?
Calibration procedure for electro magnetic flow meter
why we are using analytical instrument in plant ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)