what is meant by neutral Ct of a transformer and how it
connected in transformer
Answers were Sorted based on User's Feedback
Answer / dinakaran
Normally neutral is connected to the earth.In that neutral
line we are connecting ct bcoz of sensing the earth fault to
protect the transformer winding against earth fault.
| Is This Answer Correct ? | 33 Yes | 2 No |
Answer / vinod
Neutral CT is connecting between the neutral of transformer
and earth.(neutral bush of T/F to CT P1, CT P2 to earth).
This CT (PS Class) out put is using for REF (Restricted
earth fault protection of transformer winding)ie.REF is
operate only winding earth fault
| Is This Answer Correct ? | 10 Yes | 3 No |
Answer / md ekram
Normally neutral is connected to the earth.In that neutral
line we are connecting ct bcoz of sensing the earth fault to
protect the transformer winding against earth fault.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / amal raj
neutral is connected to the earth.In that neutral
line is connecting ct for sensing the earth fault to
protect the transformer winding against earth fault.
| Is This Answer Correct ? | 2 Yes | 0 No |
What is difference and reason b/w -48V BTS system and 24 V BTS system. Plzzzzzzzzz tel me.
What happens if we give ac supply to dc shunt and series motors individually
We've 2 diffrent DG's with same capacity (500 KVA). Can we sync them ?
what is the reason for indication of light in the earth lamps of main switchboard.if there is an earth why does one lamp get dim and the other two bright.
do we convert single phase line to three phase at minimum cost?
Why CT secondary should not left open??????????
can anyone plz tell me in 3 phase induction motor, whare we use STAR CONNECTED MOTOR and whare we use DELTA CONNECTED MOTOR
like the transformer another electrical static device which operate on same priencipal?
13 Answers Power Grid, Vishal Transformers,
Why a single-phase induction motor not an inherently self-starting machine?
11 Answers ETC, Hindustan Shipyard,
What is the difference between grid and off- grid system??
WHAT HAPPENING TO TRANSFORMER???? i have the step down transformer rating 230/12v, power rating something.,,, ok. suppose iam giving 12v to secondary side,what will happen on primary side.,,,
What are the specifications for getting approval of Substation?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)