Answer / dinakaran
Normally neutral is connected to the earth.In that neutral
line we are connecting ct bcoz of sensing the earth fault to
protect the transformer winding against earth fault.
| Is This Answer Correct ? | 33 Yes | 2 No |
Answer / vinod
Neutral CT is connecting between the neutral of transformer
and earth.(neutral bush of T/F to CT P1, CT P2 to earth).
This CT (PS Class) out put is using for REF (Restricted
earth fault protection of transformer winding)ie.REF is
operate only winding earth fault
| Is This Answer Correct ? | 10 Yes | 3 No |
Answer / md ekram
Normally neutral is connected to the earth.In that neutral
line we are connecting ct bcoz of sensing the earth fault to
protect the transformer winding against earth fault.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / amal raj
neutral is connected to the earth.In that neutral
line is connecting ct for sensing the earth fault to
protect the transformer winding against earth fault.
| Is This Answer Correct ? | 2 Yes | 0 No |
How to calculate the cross section area for a 350 m cable, motor power is 26 kw???
A 25MVA 3300/400V T/F is termed as per winding is …… a) primary 3300V & Secondary 400V b) primary 3300V & low voltage winding 400V c) High voltage winding 3300V & Secondary 400V d) High voltage winding 3300V & low voltage winding 400V
4 Answers Engineers India Limited,
WHAT SHOULD BE THE BEST CURRENT RATINGS (PRIMARY / SECONDARY)FOR A CT INSTALLED AT THE INCOMING 11KV PANE? WILL IT BE CALCULATED ON THE BASES OF MAXIMUM DEMANT VALUE OR ON SUM OF ALL TRANSFORMER'S KVA? NOMALLY MAX DEMAND REPRESENT THE MAXIMUM OPERATING LOAD OF THE PLANT AND TOTAL KVA OF (SAY 5 NUMBERS TRANSFORMERS) REPRESENT THE CONNECTED LOAD. WHICH i.e. MAX DEMAND KVA OR CONNECTED KVA ARE BETTER TO USE FOR CT CURRENT CALCULATION? PLEASE ANSWER.
how can we change the rotating direction of single phase AC induction motors?
12 Answers Heubach Colour, L&T, MNM Jain Engineering College,
What is difference between safe PLC and normal PLC
What is the meaning of Insulation H for transformers????
advantage,disadvantage,aplication of sensorless direct torque control of induction motor
why ct ratio always rated 5.
What does the term supermesh means?
Any one who apply for Ferro Scrap Nigam Limited cn join with me at rajuhalder@indiatimes.com or 09669717028
Can we use a window type neutral CT instead of a bar type neutral CT. We have an issue with a neutral bar type CT of 800/1 ratio with a Circuit breaker NS800L shneider type, and we want to change it with a window type. Pls advise. Thanks
why are installed water leakage detection system data centers & server rooms
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)