what is meant by neutral Ct of a transformer and how it
connected in transformer
Answers were Sorted based on User's Feedback
Answer / dinakaran
Normally neutral is connected to the earth.In that neutral
line we are connecting ct bcoz of sensing the earth fault to
protect the transformer winding against earth fault.
| Is This Answer Correct ? | 33 Yes | 2 No |
Answer / vinod
Neutral CT is connecting between the neutral of transformer
and earth.(neutral bush of T/F to CT P1, CT P2 to earth).
This CT (PS Class) out put is using for REF (Restricted
earth fault protection of transformer winding)ie.REF is
operate only winding earth fault
| Is This Answer Correct ? | 10 Yes | 3 No |
Answer / md ekram
Normally neutral is connected to the earth.In that neutral
line we are connecting ct bcoz of sensing the earth fault to
protect the transformer winding against earth fault.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / amal raj
neutral is connected to the earth.In that neutral
line is connecting ct for sensing the earth fault to
protect the transformer winding against earth fault.
| Is This Answer Correct ? | 2 Yes | 0 No |
what is the use of Turbocharger in a gen-set?
how to choose the cable rating for load (KW)? EXAMPLE.50KW load
14 Answers ACC, NCUI, Polycab, PowerSol, Siemens, SW,
what is meant by impedance testing of transformer and why it is used
WORKING PRINCIPLE OF HALOGEN LAMP & MEQUERY LAMP
Can neutral line also be use as a earthting for distribution transformer, or we need separate earthing pit forh the transformer?
Why the output of generator varies eventhough the shaft speed is constant in thermal power plant?
Briefly define and explain the following different types of Pulse Amplitude Modulation (PAM) with some examples. i) 2-PAM ii) 4-PAM iii) 8-PAM iv) 16-PAM v) Quadrature Amplitude Modulation (QAM)
What is the bundle conductor?
1.What is the difference between isolators and circuitbreakers? 2.What is bus-bar?
current transformer cannot measure voltage or not ? then y we use P.T ?
If u take a kWh reading in 11 kV HT and 440 LV side at same time in yesterday today , then why LT consumed units 3-4℅ high as compared to HT units
why 3 phase is converted into 2 phase using electronics circuit why not 2 phases are diresctly putted from the 3 phase transformer??
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)