To find closed tank level by DP transmitter , how to
findout its range.and insomeplace they using range like -
1500 to +1500 mmwc why not 0 to 3000 mmwc. how they spilit
they range for minus and plus.and why?
Answer / yashwant
THIS IS LEVEL MEASUREMENT USING DP TRANSMITTER, CLOSE TANK
MEANS PRESSURIZED ,PRESSURE IS EVERY WHERE IN SIDE TANK WILL
BE SAME. LOW SIDE WILL BE TOP SIDE WHERE ALL CONDENSATE
COLLECTED THIS IS REFERENCE SIDE, NOW ON OTHER HAND HIGH
SIDE WILL BE LOWER, DIFFERENTIAL PRESSURE OBSERVED AT DPT.
LOWER SIDE WILL BE ALWAYS FULL IE FULL SCALE IF YOU ARE
HAVING TANK HEIGHT 1500 MM THEN PRESSURE AT LOWER SIDE IS
1500 MMWC. AND THAT OF HIGHER SIDE WILL BE THE ACTUAL WATER
INSIDE TANK WE SAY 500 MMWC STEAM PRESSURE WILL BE EVERY
WHERE SAME SO NO NEED TO CONSIDER PRESSURE INSIDE THE TANK.
MINUS AND PLUS WILL BE JUST FOR HAVING DIFFERENCE IN TWO
COLUMN IE HP AND LP. ALSO TANK IS NOT PRESSURIZED YOU CAN
USE PRESSURE TRANSMITTER CALIBRATED IN YOUR RANGE (HEIGHT OF
TANK MMWC)
| Is This Answer Correct ? | 6 Yes | 4 No |
Relation in MMWC to Flow rate
Using your own examples solve a problem involving normal table. (experimental method and analysis)
What is difference between loop and zone ?
The DCS has the following signal type:
TEMPERATURE VARIATION FOR FREQUENTLY.
I am having a Phoenix digital to modbus converter. The o/p of the same is connected to flow computer FB407. But the digital signals are updated only after one minute in the flow computer. what may be the cause of delay in communication? Flow computer is having a scanning period of less than 1 sec.
what is earthing ,grounding in c&i panel?what is the resistance in earthing and grounding of c&i panel?what do u mean by shielding and what is its resistance?
Can we place a Control Panel in Hazardous area Group IIC ? If 'yes' then is there any approval required? If 'yes' then there is any specific IP rating or any standard required? If 'Yes' What is MOC of control panel?
1,why we use 4-20 ma output of all instrument qhy not use 0- 20, 2,what is the different between PLC & DCS. 3,how can we meaure maximum span of new flowmeter if not given any information.
What is the use of control cable?
use of split range ? where it is used ? in which control loop it is used ?
Draw a P& ID showing – orifice flange, plate, dp transmitter, isolation & bypass valves and tubing.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)