How to decide the input and output circuit breaker for a
1600kva transformer.Is there any calculation is involved.
Answers were Sorted based on User's Feedback
Answer / basayya
1600kva transformer
p= root3*v*i*cospai 1600kva*1000=1600000
1600000/1.732*400*1=2309.46
total current= 2309.46
u can use transformer sec side acb 2500A
i think
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / rajeshsan
The circuit breaker is selected based on following factors.
1. Voltage level
2. Fault current.
3. Type of Breaker.
4. Operating Time.
5. Number of operations.
| Is This Answer Correct ? | 1 Yes | 0 No |
it depends on the condition where transformer is put into
the service in the power systems because impedence vary
with these so fault current also varies
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / lokesh ranjith
Depend upon the contract demand the transformer will be
nstalled for full load ex: input will 850AVCB
output will be 2500A
| Is This Answer Correct ? | 4 Yes | 4 No |
Answer / baskaran.r
the high voltage side the rating will be according to fault
level of the system and primary current. the secondary
rating also according to the full load current of the
transformer
| Is This Answer Correct ? | 2 Yes | 3 No |
how earth resistance can be improved in dry soil
16kv transformeris stolen in my village.and department is not taking action.then what should i do.any shortcut .please help any idea
Re: how to calculate diesel consumption of a D.G.Set? Answer # 1 We can not calculate the diesel comsumption...depending upon load it will conume the diesel...suppose the 1500kva D.G is running and the load is 1000kw means it will consume 150-200 liters per hour....
Why we are using LA Rating 10kA in 66 kv substation
What is the function of a capaitor in 1-phase IM?
Multi-step core is used in transformer to: A) Increase the output B) Decrease the cost of core material C) Decrease the cost of copper D) Increase the efficiency
when a three phase motor in running condition consumes 2A in each phase,and if one of the phase gets fails what will be the consumption in other two phases
WHY IS THE POWER FACTOR NOT MORE THAN UNITY.
why do we use 25kv supply for traction purpose
where HT & LT capacitor uses ?
how can we calculate ct ratings ?its any formula ?
can any tell me how to do wiring connection in L&T 3ph 4wire E301 CT operated energy meter, what is P1,P2,P3,P0. M1,M2,M3, L1,L2,L3.
2 Answers Bhartiya International,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)