How to decide the input and output circuit breaker for a
1600kva transformer.Is there any calculation is involved.
Answers were Sorted based on User's Feedback
Answer / basayya
1600kva transformer
p= root3*v*i*cospai 1600kva*1000=1600000
1600000/1.732*400*1=2309.46
total current= 2309.46
u can use transformer sec side acb 2500A
i think
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / rajeshsan
The circuit breaker is selected based on following factors.
1. Voltage level
2. Fault current.
3. Type of Breaker.
4. Operating Time.
5. Number of operations.
| Is This Answer Correct ? | 1 Yes | 0 No |
it depends on the condition where transformer is put into
the service in the power systems because impedence vary
with these so fault current also varies
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / lokesh ranjith
Depend upon the contract demand the transformer will be
nstalled for full load ex: input will 850AVCB
output will be 2500A
| Is This Answer Correct ? | 4 Yes | 4 No |
Answer / baskaran.r
the high voltage side the rating will be according to fault
level of the system and primary current. the secondary
rating also according to the full load current of the
transformer
| Is This Answer Correct ? | 2 Yes | 3 No |
Can anyone provide with a SLD for HT panel installation for a 33KV line and distribution end has three 1.5MV transformers. Is it suitable to use OCB or VCB and also provide me the suitable rating and its connection diagram.
What are your future plans for the company if permanently employed?
diffance between eletrical and eletronics?
what is a speed of rotor when we give supply to stator of 50hz and as well as rotor of 60hz of an induction motor?????
why HT voltage rating in multiple of 11
what is the calculation of current when a clampmeter is attached to two phases of any drives.
What will happen if the oil level in the buchholz realy of a transformer gets down?
How to calculate mf when meter equipment and meter are connected
can we coorect P.F. OF 320 KVA ALTERNATOR AT LOCAL SITE WITH RATED .8 PF LAGGING.
how to compare with Relay settings for HT< panels, RMU panel, and PSS CSS transformer?? 1) Load amps, 2)Tripping time, 3) CT ratio, 4)Cable size 5) Transformer KVA rating 6) transformer full load amps
33kv Rated output avilable in market (any where in india)
Haw to check conductivity of budbar
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)