How to decide the input and output circuit breaker for a
1600kva transformer.Is there any calculation is involved.
Answers were Sorted based on User's Feedback
Answer / basayya
1600kva transformer
p= root3*v*i*cospai 1600kva*1000=1600000
1600000/1.732*400*1=2309.46
total current= 2309.46
u can use transformer sec side acb 2500A
i think
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / rajeshsan
The circuit breaker is selected based on following factors.
1. Voltage level
2. Fault current.
3. Type of Breaker.
4. Operating Time.
5. Number of operations.
Is This Answer Correct ? | 1 Yes | 0 No |
it depends on the condition where transformer is put into
the service in the power systems because impedence vary
with these so fault current also varies
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / lokesh ranjith
Depend upon the contract demand the transformer will be
nstalled for full load ex: input will 850AVCB
output will be 2500A
Is This Answer Correct ? | 4 Yes | 4 No |
Answer / baskaran.r
the high voltage side the rating will be according to fault
level of the system and primary current. the secondary
rating also according to the full load current of the
transformer
Is This Answer Correct ? | 2 Yes | 3 No |
An impedance of 100 ohms resistance and an unknown inductance is connected across the capacitor. The resulting impedance is a pure resistance of 500 ohms ifω = 10^5 rad/sec. calculate the values of inductor and capacitor.
What are the basic elements used for modeling mechanical translational system?
A simple Question from all.... If Voltage drops then its rated value what will be effect on a Residential load? similarly if voltage rises from its rated value then what will be effects on a load? i know if voltage drops the equipment or device draws more current then its rated what are other reasons ? thanks in advance for ur time.......
suppose generator rating is 50 kw,load is 25 kw,hw much d generator ll generate?what about d remainin power?
Difference between SFU & FSU with advantantages & drawback?
Why not LED burn after showing alarm,as Alarm volt is 11- 13,But LED is of3 volt,why it isnt Burn??
How do we calculate Blower drive Power (kw) If we have Volume m3 and Pressre (mmWC)
If a motor of 8.5 KW with same load and using in both Star & Delta one by one,then which will take more current in star connected or in delta connected
how to calculate the size of cable tray
how to compute kvar in substation feeder to improve power factor and sending voltage
UG cable sizes were specified in sqmm. But practically its not coming to mesure. What's the reason for that? And how they specify the size of the cable?
How to select cable the size, what is the parameters use and what is the formulas use for this cable size calculation?