how to measure earth pit resistance
Answers were Sorted based on User's Feedback
Earth pit resistance is measured by Earth tester, Earth
tester have four terminals P1,P2,C1,C2 i.e. Two potential &
Two Current terminals. while earth pit testing, P2 & C2 are
shorted and C1 connected to current spike(Conductive rod)
which should be drived into soil at around 30 meter
distance from earth pit and P1 is connected to potential
spike(Conductive rod) drived at around 15 mtr away from
earth pit in the direction of current spikes.By rotating
the handle of meter(in old meters) or by pressing test
button (in new type meter) one can get earth resistance.Now
Potential spikes are drived at different locations toward
earth pit and current spike side and a curve between
distance and resistance is plotted. Earth resistance will
be platue of the graph.In this meter current is passed
between earth pit and current spike and potential is
measured between potential spike and earth pit. Ratio
between Voltage measured and current passed thrugh the
earth is the resitance of earth pit.
| Is This Answer Correct ? | 139 Yes | 20 No |
Answer / satya narayan padhy
Earth pit resistance is measured by Earth tester, Earth
tester have four terminals P1,P2,C1,C2 i.e. Two potential &
Two Current terminals. while earth pit testing, P2 & C2 are
shorted and C1 connected to current spike(Conductive rod)
which should be drived into soil at around 30 meter
distance from earth pit and P1 is connected to potential
spike(Conductive rod) drived at around 15 mtr away from
earth pit in the opposite direction of current spikes.By
rotating
the handle of meter(in old meters) or by pressing test
button (in new type meter) one can get earth resistance.Now
Potential spikes are drived at different locations toward
earth pit and current spike side and a curve between
distance and resistance is plotted. Earth resistance will
be platue of the graph.In this meter current is passed
between earth pit and current spike and potential is
measured between potential spike and earth pit. Ratio
between Voltage measured and current passed thrugh the
earth is the resitance of earth pit.
| Is This Answer Correct ? | 25 Yes | 10 No |
Answer / salman hazari
Earth pit testing is measured by megger or earth pit tester. There are 4 terminals in megger. P1, P2, C1, C2, it means there are two potential terminals and two current terminals. while measuring earth pit resistance we have the requirement of 3 wires. one wire will be connected between one earth electrode which has drived in ground and P1 point of tester from a distance of 30 meters from earth pit. 2nd wire will be connected between one earth electrode which has drived in ground and C1 point of tester from a distance of 15 meters from earth pit. Both electrodes in opposite direction. Shorted P2 & C2 terminal by a small piece of wire. connect one wire to the Earth pit from shorted wire. Move the handle of megger. you will get the resistance value. As theoretically value should be 0 ohm. But practically it should be less then 1 ohm.
Thanks
salman Hazari
chief Engineer
Keys hotel
pimpri, pune
| Is This Answer Correct ? | 14 Yes | 1 No |
Answer / upen
It's measure by earth tester it must less then 1mega ohm 0.02 is better
| Is This Answer Correct ? | 11 Yes | 12 No |
Answer / susanta paul
Earth pit resistance is measured by Meggar.This measurement will be done on every year once in the site.
| Is This Answer Correct ? | 9 Yes | 15 No |
The advantages of Magnetic flux leakage technique over Ultrasonic technique for non distructive testing of material.
why dhyedration test required for transformer oil once in a year
why inductivedrop in dc motor neglected
How to check op amp using multimeter
What is effect of over voltage and under voltage on ACB
what is reactive power?, why its measured in VA ? is it transient behavior of system?
what types of load we get from the national grid? is this capacitive or inductive?
How can we Run three phase motor when only single or two phase supply is available ??
What are the protections for safe running of electric generator?
what is meant by vector group of a transformer? How can it be derived?
what is the instrument used for measuring insulator RESISTANCE
Can we put 3 layers of cable tray while installing tray
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)