how to measure earth pit resistance
Answers were Sorted based on User's Feedback
Earth pit resistance is measured by Earth tester, Earth
tester have four terminals P1,P2,C1,C2 i.e. Two potential &
Two Current terminals. while earth pit testing, P2 & C2 are
shorted and C1 connected to current spike(Conductive rod)
which should be drived into soil at around 30 meter
distance from earth pit and P1 is connected to potential
spike(Conductive rod) drived at around 15 mtr away from
earth pit in the direction of current spikes.By rotating
the handle of meter(in old meters) or by pressing test
button (in new type meter) one can get earth resistance.Now
Potential spikes are drived at different locations toward
earth pit and current spike side and a curve between
distance and resistance is plotted. Earth resistance will
be platue of the graph.In this meter current is passed
between earth pit and current spike and potential is
measured between potential spike and earth pit. Ratio
between Voltage measured and current passed thrugh the
earth is the resitance of earth pit.
Is This Answer Correct ? | 139 Yes | 20 No |
Answer / satya narayan padhy
Earth pit resistance is measured by Earth tester, Earth
tester have four terminals P1,P2,C1,C2 i.e. Two potential &
Two Current terminals. while earth pit testing, P2 & C2 are
shorted and C1 connected to current spike(Conductive rod)
which should be drived into soil at around 30 meter
distance from earth pit and P1 is connected to potential
spike(Conductive rod) drived at around 15 mtr away from
earth pit in the opposite direction of current spikes.By
rotating
the handle of meter(in old meters) or by pressing test
button (in new type meter) one can get earth resistance.Now
Potential spikes are drived at different locations toward
earth pit and current spike side and a curve between
distance and resistance is plotted. Earth resistance will
be platue of the graph.In this meter current is passed
between earth pit and current spike and potential is
measured between potential spike and earth pit. Ratio
between Voltage measured and current passed thrugh the
earth is the resitance of earth pit.
Is This Answer Correct ? | 25 Yes | 10 No |
Answer / salman hazari
Earth pit testing is measured by megger or earth pit tester. There are 4 terminals in megger. P1, P2, C1, C2, it means there are two potential terminals and two current terminals. while measuring earth pit resistance we have the requirement of 3 wires. one wire will be connected between one earth electrode which has drived in ground and P1 point of tester from a distance of 30 meters from earth pit. 2nd wire will be connected between one earth electrode which has drived in ground and C1 point of tester from a distance of 15 meters from earth pit. Both electrodes in opposite direction. Shorted P2 & C2 terminal by a small piece of wire. connect one wire to the Earth pit from shorted wire. Move the handle of megger. you will get the resistance value. As theoretically value should be 0 ohm. But practically it should be less then 1 ohm.
Thanks
salman Hazari
chief Engineer
Keys hotel
pimpri, pune
Is This Answer Correct ? | 14 Yes | 1 No |
Answer / upen
It's measure by earth tester it must less then 1mega ohm 0.02 is better
Is This Answer Correct ? | 11 Yes | 12 No |
Answer / susanta paul
Earth pit resistance is measured by Meggar.This measurement will be done on every year once in the site.
Is This Answer Correct ? | 9 Yes | 15 No |
IF DISTANCE IS 100METERS B/W AMP.METER AND CURRENT TRANSFORMER WHAT WILL BE AFFECT IN ACCURACY .METER CAN SHOWING ACCURATE CURRENT OR NOT IF NOT WHAT CAN I DO TO GET 100% ACCURACY.
what happens in a genarator when rotor supplied with ac instead of dc
DESCRIBE THE CONSTRUCTION ANDOPERATION OF BELT CONVEYORS AND SCR CONVEYORS , DRAW NEAT SKETCHES
why leading pf indicates a negative sign???
Please clarify, 1. Is it required to lay two runs of GI wire along with Armoured LT cable if it is laid between one big mains (63Amps TPN SDF) to small main (32A TPN SDF) with proper glanding termination? 2. If the armoured cable with proper glanding is laid from DB to CNC machine, is it required to run two runs of body earthing to the Machine from DB? 3.If the armoured cable with proper glanding is laid from Substation to Hangar, distance is approx. 100 mtrs, is it required to do earthing at shop area though the primary termination at substation is earthed through gland.
Ohm's law applicable for semi-conductors?
What is the difference between earth and neutral
What is PTZ Camera???
3 Answers Cherrytec, CSC, Honeywell, Zicom,
In electrical cables what is U and U0 refers?
I am applying for NTPC examination.Can we please provide previous paper to my mail prasad.chintala108340@gmail.com
What is the difference between harmored cabled and unharmored cables
WHAT IS THE WINDING PROCEDURE OF ELECTRICAL MOTOR